In a thermal power plant ID Fans running with full load but
boiler load is only 80 % give reason ?
Answers were Sorted based on User's Feedback
Answer / lalitshukla
there are many reason for that.
1. furnace or any duct of flue gas leakage.
2.deposition on super heater which clog the passage of flue gas
3.density of fuel below required density of boiler fuel
| Is This Answer Correct ? | 22 Yes | 3 No |
There will be soot deposits on outer surface of boiler tube
| Is This Answer Correct ? | 17 Yes | 6 No |
Answer / mohamed elnakib
it is due to the air preheater being clogged increasing the
load of the ID fans due to the bad suction and this clogging
is mostly due to the baskets being melted due to the
formation of the ACIDS from the exhaust gases and the dew
point effect .
this is the only logical reason for why the ID fan is 100%
loaded while the boiler is not .
| Is This Answer Correct ? | 12 Yes | 2 No |
May be...
1.APH tube leakage
2.Boiler ducting leakage
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / y v subba rao
If the moisture content in fuel is more than designed fuel, id fans has to run at full rpm to sent out the additional water vapor produced from the additional moisture. In fact total flue gas quantity was increased
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ns satyaraj
Provided Id inlet damper is fully opened main reasons are
1 more gases are being handled . Happens when due to infiltration of external air into ducting thru leakages
Fluegas path are clogged at some place, such as at APH, superheater, economiser
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a k handa
Coal feeding may not be as per the required load.
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / alan
the IDF inlet damper may be stocked to fully open.
| Is This Answer Correct ? | 2 Yes | 3 No |
what is the trip circuit supervision in an electrical meaning?
Is it not bad to bleed steam from turbine stages before utilizing its energy.
What is Droop Control in Woodward?
line safety is not opening but drum safety opens what to do?
What will happen if the Air Preheater is placed before the Economiser?
6 Answers Bhel, KSPL, Tata Power,
what is under voltage protection 27
.What is drip and drain.
whats plant?
what is actual CAL MODE & cal means?
What do mean by 3t
1 Answers Aman, Birla, Grasim,
operation
Looking for Bently Nevada surplus 3300/52-01-00-00 Reverse Rotation Monitor , 4 pieces.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)