In a thermal power plant ID Fans running with full load but
boiler load is only 80 % give reason ?
Answers were Sorted based on User's Feedback
Answer / lalitshukla
there are many reason for that.
1. furnace or any duct of flue gas leakage.
2.deposition on super heater which clog the passage of flue gas
3.density of fuel below required density of boiler fuel
| Is This Answer Correct ? | 22 Yes | 3 No |
There will be soot deposits on outer surface of boiler tube
| Is This Answer Correct ? | 17 Yes | 6 No |
Answer / mohamed elnakib
it is due to the air preheater being clogged increasing the
load of the ID fans due to the bad suction and this clogging
is mostly due to the baskets being melted due to the
formation of the ACIDS from the exhaust gases and the dew
point effect .
this is the only logical reason for why the ID fan is 100%
loaded while the boiler is not .
| Is This Answer Correct ? | 12 Yes | 2 No |
May be...
1.APH tube leakage
2.Boiler ducting leakage
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / y v subba rao
If the moisture content in fuel is more than designed fuel, id fans has to run at full rpm to sent out the additional water vapor produced from the additional moisture. In fact total flue gas quantity was increased
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ns satyaraj
Provided Id inlet damper is fully opened main reasons are
1 more gases are being handled . Happens when due to infiltration of external air into ducting thru leakages
Fluegas path are clogged at some place, such as at APH, superheater, economiser
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a k handa
Coal feeding may not be as per the required load.
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / alan
the IDF inlet damper may be stocked to fully open.
| Is This Answer Correct ? | 2 Yes | 3 No |
what's interlock relay ?
3 Answers International Mega Food Park Limited, National Power Training Institute NPTI,
what is need of primary water system in power plant?
Difference between electrical and electronics?
What should be the neutral and body grounding sysytem for grid (132 KV) parallel generators (440 volts)?
What happens if air is present in LPH and HPH.
What is MFT and when it is acted.
Why attemperation is required in HRSG in a combined cycle power plant?
line safety is not opening but drum safety opens what to do?
During shutdown of Steam Turbine,How do we cross the critical speed?
why we use reduction gear box to reduce turbine high rpm to 1500 rpm in small plant
3 Answers Maruti Suzuki, Sail,
what's the moog valve
DCS marshaling Cabinet Power supply can be replace during plant running time? Answer Yes it is possible. I am talking about the controller and cards power supply modules. They are always redundant and connected through diode so that if one power supply fails the other can take the charge immediately.so it is possible to replace one of them in running plant if the other one is healthy. MY question is how switching done.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)