what is CT saturate?and which effect on CT after its saturate?

Answers were Sorted based on User's Feedback



what is CT saturate?and which effect on CT after its saturate?..

Answer / akash rao

ct is a electricl measuring instrument

Is This Answer Correct ?    3 Yes 0 No

what is CT saturate?and which effect on CT after its saturate?..

Answer / operations

It is possible that relatively low-ratio CTs are applied for
protective relaying of small loads
fed from switchgear and motor controllers of relatively high
short-circuit capacity. Assume
the worst-case scenario of 64kA available fault current from
bus feeding a small motor load
of normal current below 50A. In theory, CTs rated as lows as
50:5 and relay class C10 may
be applied for protection purposes.
Realizing that 64kA of fault current is 1080 times the rated
current of the 50:5 CT, the
magnitude of the problem is evident. Protection class CTs
are designed to work in the linear
range, with minimal errors and minimal waveform distortion,
only up to 20 times the rated
nominal current with the burden as defined by the relay
class (saturation voltage) of the CT
per IEEE Std. C57.13.
Well-established and relatively accurate equations are
available for calculation of the
actual maximum primary current for saturation-free operation
under any specific burden,
any specific X/R ratio, and any specific residual flux in
the CTs. This engineering practice is of
little help here: A CT fed with a primary current hundreds
of times its rated current will
saturate severely - only relatively short duration peaks of
limited current will be observed
from the secondary of the CT. These peaks can be as low as
5-10% of the ratio current, and
will last a small fraction of the half-cycle, down to 1-2ms
in extreme cases. As a result only a
very small portion of the actual ratio current is presented
to protective relays fed from such
severely saturated CTs. In terms of the true RMS value, the
secondary current may be as low
as 1-2% of the expected RMS secondary current.
On the surface it may seem that a severe problem takes place
here – the fault current is
so high that it virtually stops the CT from passing the
signal to the relay. The relay does not
see enough proportional secondary current during severe
faults in order to operate its short
circuit protection. The upstream relay, using CTs of a much
higher ratio, measures the fault
current more accurately and trips. Zone selectivity is lost
because the poor low-ratio CT was
“blinded” to the fault.

Is This Answer Correct ?    3 Yes 1 No

what is CT saturate?and which effect on CT after its saturate?..

Answer / k.prakashchandra

That is magnetic saturation , there will not be increase in flux with the current . The secondary current remains constant after saturation .

Is This Answer Correct ?    1 Yes 0 No

what is CT saturate?and which effect on CT after its saturate?..

Answer / chinmay kumar patra(npti)

CT saturated means saturation of core of CT .ie total current induced is the magnetizing current so no load current no deflection.so secondary of CT should be always in closed condition otherwise it will be saturate.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Power Plant Engineering Interview Questions

what equipment is most efficient in power plant?

4 Answers   Adani,


Can any one advised me how we can measure the losses in a 11kV/415v power transformer? We have no access to the incoming mains into the primary of the transformer. Can one derive something useful by measuring temperature rise in the transformer?

1 Answers   Dexdyne,


Power plants are called CPP,IPP,LLP What is the meaning of it? And tell me some other type of powerplant names.

1 Answers  


why oil filled transformers will be with explosion and fire often?

1 Answers  


what are the major duties of a instrumentation engineer in a power plant.?

3 Answers   Gulf,






what is block out in thermal power plant?

3 Answers   SECL,


Our 8mw steam turbine (condensing cum extraction) exhaust steam temperature is high even after taken it in hogger why

1 Answers   Bombay Rayon Fashions,


By any way can we increase the B check hours from 300 to 500

0 Answers  


What is the over speed in turbine? What is critical speed?

3 Answers  


What is difference between Actual Drum Level and Compensated Drum Level?

2 Answers   DVC,


63.5 ohm NGR is connected with our gas engine genrator running at 500 rpm, 50 hz and synched with WAPDA at 6.3 KV bus voltages, 2500A and 25KA(1 sec). can some one give me proper calculations how it comes 63.5ohm?????

2 Answers   UET,


LAPT working in alternator / generator

0 Answers   Power Plant,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)