Difference between directional earth fault and
non-directional earth fault
Answers were Sorted based on User's Feedback
Answer / manesh s
Directional Earth Fault is the Fault(between Phase/s to
Earth)in the system,if system is using only one source, so
Fault would be in one direction(towards the system)
where as Non-Directional Earth Fault is the
Fault(between Phase/s to Earth)in the system,if system is
using two or more source, so Fault would be in two
direction(away or towards)
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / jerry smith
Directional Earth Fault detection is used to isolate a
fault, when using more than one source of power input.
Current Transformers are used to verify the net sum of
current as zero between any two sources of power. If there
is a fault, the breaker between the power sources is
OPENED. The protection logic will then see if the fault has
cleared. If the fault has cleared, the fault is on the side
with ungrounded power source, and will protection logic
will trip the ungrounded power supply. Conversely if the
fault continues to flow after the bus tie is OPEN, then the
fault is on the side of the grounded power supply, and the
grounded power supply will be tripped.
Non-directional Earth Fault would be a simple fault
detection, as located on a generator neutral.
| Is This Answer Correct ? | 2 Yes | 4 No |
What is reheater protection based on what mft will be act on RH protection
can dp type level transmitter work in under vaccum condition
how to differentiate between "ALL fuel lost" and "All Fuel Lost" in Boiler MFT condition?
How to control cooling tower alge
1 Answers GPL, SPY Agro Industries,
What is the the sequence/logic of burner management system in boilers. What is purging and scavenging?
What is excitation current and voltage in hydro power plant ?
How to calculate power press toneage
What happens if there is no HP and LP By-pass.
can u please tell me how to calculate the concrete quantity for a under reamed pile? r=300mm,depth=3m for a cylinder and for bulb l=.750mm,width=.525
our 125 kva DG does not start in AUTO mode works normally in MANUAL mode please give me a solution.....
.What are the equipments should run when there is a black out in power plant.
operation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)