how many safeties should be present in boiler?what are they?
Answers were Sorted based on User's Feedback
Answer / bhola shnaker
there are 2 to 6 numbers of safety valves (SVs) on the boiler.
Around 2 Nos on Drum, of one high and one low setpoint.
Around 2 Nos on Superheater Steam Line of one high and one low setpoint.(but less then Drum SV setpoint, to avoid starvation of SH main steam line)
around 2 Nos on reheater line (if reheater is provided)
Apart from it 1 No of EMRV on the HP superheater line, setpoints below that of Safety valves of the lines.
Also we have Relief valves on he HP econimiser, which acts as a Over protection valve (against Pressure)
Remember SVs are Differnt from Relief valves, as RVs are used on liquid whereas SVs are used on Steam line.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / arun
Totally 9 SV are There
Drum - 3 ( left side-1 , right side-2 )
SH Outlet( MS Line ) - 2
RH Inlet - 1
RH Outlet - 3
This is for BHEL 210MW Boiler
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / powerplant.calculations
Boiler interlocks:
1-High & low drum level trip
2-High furnace draught trip
3-Safety valve
4-Boiler explosion vents
Also refer following link to get more information on Boilers
https://www.powerplantandcalculations.com/2020/06/why-how-these-in-boilers.html
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pandian
only 6 safety valves used in reheater boilers normally small capacity boiler used 4 safety valves
| Is This Answer Correct ? | 0 Yes | 1 No |
what is IR in differential test on motor?
How to decide Heating surface area of boiler on their steam generating capacity?
What is indipendant power plant
dear sir i have completed one year post diploma certificate in thermal power engineering from national power training institute durgapur ...plz suggest me for power sector job
63.5 ohm NGR is connected with our gas engine genrator running at 500 rpm, 50 hz and synched with WAPDA at 6.3 KV bus voltages, 2500A and 25KA(1 sec). can some one give me proper calculations how it comes 63.5ohm?????
why is the in steam turbine axial displacement of active side thrust pad is positive and non active side thrust pad is negative.
im try to calculating seawater flow required for SW-FGD system. I need a guide, equation or method to do it, can some one help me! Thanks very much
LAPT working in alternator / generator
1.what is the reason for transformer and lightning arrester blast in 33kv system
1 Answers Afghan Telecom, Integra, Sanghi,
procedure of how to generate power in solar plant.
What happen when the AVR of the generator fails? Will it cause power instability and total failure of the alternator?
What is MFT and when it is acted.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)