What is RTCC panel and why it is required
Answers were Sorted based on User's Feedback
Answer / perservance
RTCC means relay tap changer circuit,these are the relays
which give command to the tap changer present in the
transformer H.T side to either increse or decrese the tap
since due to inductive load ( lagging p.f ) , the secondary
terminal voltage would decrease which would not be good for
the loads so by chnging taps, we increase the primary
voltage which in turn changes the secondary
voltage,normally done online.
Is This Answer Correct ? | 235 Yes | 74 No |
Answer / xyz
RTCC means- Remote tap changing controler and it is used to
maintain the stable output voltage of the transformer by
changing the taps because we need costant voltage then only
rtcc is required
Is This Answer Correct ? | 159 Yes | 16 No |
Answer / rashid abdul rab
RTCC panel also known as AVC Panel (Automatic Voltage
Control Panel), is used to control the Transformer tap
Changer to adjust the tap position, as per the load
Is This Answer Correct ? | 115 Yes | 20 No |
Answer / shiva sharana
RTTC MEANS REMOTE TAP CHANGING CONTROL IT IS USED TO
COMMAND THE OLTC PANEL CONTROL THE PRIMARY SIDE OF
TRANSFOMER . WHEN WE REQUIRD CONSTANT VOLTAGE IT IS REQUIRED
Is This Answer Correct ? | 59 Yes | 10 No |
Answer / dipak patil
RTCC stands for "Remote Tap Changer Control". RTCC panel
is used to give operation command to OLTC(On Load Tap
Changer)of Power Transformer from remote end.
Is This Answer Correct ? | 48 Yes | 9 No |
Answer / bala
RTCC panel is called as the Remote Tap Changer Circuit. it
is used to control the OLTC Tap changer from the control
room or control point itself where RTCC panel is Placed. it
is used to get the stable output voltage.
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / chetan
RTCC MEANS REMOTE TAP CHANGING CIRCUIT. AND REQUIRED FOR
CHANGING THE TAP AT THE HV SIDE OF THE TRANSFORMER ONLINE
IF THE LV SIDE VOLTAGE OF THE TRANSFORMER FLUCTUATE
BEACAUSE OF LOAD. IT HAS AVR (AUTOMATIC VOLTAGE REGULATOR)
TO CONTROL THE TAP CHANGING.
Is This Answer Correct ? | 19 Yes | 5 No |
Rtcc is remote tap changer circuit. It is used to change tap position as per requirement of load. It generally maintains voltage at specific value, if there is any change in voltage rtcc gets it at reqd value.
Is This Answer Correct ? | 9 Yes | 3 No |
RTCC means REMOTE TYPE TAP CHANGING CONTROL panel,it is
used in transformer for tap changing.It contains an AVR
(Automatic voltage regulator),Relays and contactor for
motor.
Is This Answer Correct ? | 22 Yes | 17 No |
What is LSIG ?
how can we can take BDV test in transformer?
ratings of lightning arrester
If a contactor need to replace with faulty one. what I want to check?
what is the difference between electrical & electronics
245 Answers Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,
hi, could someone help me to find a control design for syncronising panel .
i will applied in 1U-1W on 440 volt primary delta side. what is the result of magtic balance test
how to calculate the capacity of the AC motor
which is more dangerous AC\DC supply
Why transformer is rated in kva?
what is the full form of KVAR
What is slope...? Explain slope 1 and slope 2...?