What are the consequences in using existing step up
transformer (primary 6.6kv/175A, secondary 480v/2405A) for
step down transformer to have a 6.6kv output?
Answer / blake australia
The only real limitations on a transformer are overvoltage
and heating. Using the transformer to step up instead of
step down will make no difference. However, the protection
relay settings for this transformer, and some other parts
of the network, will need to be changed.
Is This Answer Correct ? | 3 Yes | 1 No |
it says in neutral wire current flows under normal condition, but when we put tester it wont glow, why?
what is the difference between electrical & electronics
245 Answers Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,
What is the purpose of Rotor earth fault relay and How to test the Rotor earth fault relay in generators and What is the procedure?.
DEAR ALL I have motors ( 10 units )each one is 90kw 380V 50 HZ 1000rpm but new local pwer is 220v 60 hz requierd rpm should be 1000 pleas what the beast solution is used frequncy converter or rewinding all motos or chang all motors thanks
why bucholtz relay placed inclined in transformer?
In DC current-excitation to transformer, why it sucks more current? Eventhough there is no power transfer between primary and secondary? R is very low so it should suck less current only na thn y its current increases?
what's the different between ELCB, ELR and ELS?
where is used dc volage transformer,and what is highest capacity of transformer
what is power factor when in view of a lineman
1.stranded resistance values of motors? 2.how to calculate the resistance values of single phase and 3phase motors?
what type of motor is used in washing machine
what is the Excaste meaning of CT Saturation?? 10 P 20, 15 VA, what is the meaning of 10, & 20. if the CT polarrity changed what will happened?? what is the differece between measuring CT & Protection CT?? what is the Saturation Point of measuring CT & Protection CT??