Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what are the difference between protection class CT and
Class PS CT

Answers were Sorted based on User's Feedback



what are the difference between protection class CT and Class PS CT..

Answer / siddharth agasti

class ps ct is a protection class ct.it is used for
differtial proction,distance proction.

Is This Answer Correct ?    47 Yes 4 No

what are the difference between protection class CT and Class PS CT..

Answer / chetan joshi

Protection class CT are 5 p10 and 5 p 20 and PS class ct
are used where neutral point is available such that star
conneccted secondary of Transformer and alternator ,it is
used for differential protection.

Is This Answer Correct ?    25 Yes 9 No

what are the difference between protection class CT and Class PS CT..

Answer / shivaji mangalagiri

all the protection cts like over current
relay and earth fault relay of transformer,Alternator and
HT motors are having core 1 and core 2 options. CLASS PS
type is used only for differential protection purpose of
transformer,Alternator and
HT motors only. and this type of cts are available only in
PAIR SCHEME (PS) AND their turns ratios,
impedances, VA burdens, knee point etc all these critical
parameters are exactly matched with each other.

Is This Answer Correct ?    18 Yes 4 No

what are the difference between protection class CT and Class PS CT..

Answer / s.rajasekar

the saturation point between the ps is higher than
protection class & metering.and the accurracy is also
higher then protection CT. It has highly efficient so it is
mosly used in sofasticated protections ( REF,DIFF,DISTANCE )

Is This Answer Correct ?    9 Yes 1 No

what are the difference between protection class CT and Class PS CT..

Answer / patel indukumar

Protection class is ued in protection like over current
relay and earth fault relay of transformer,Alternator and
HT motor.PS class is used in DIfferential protection like
transformer,Alternator and HT motor.

Is This Answer Correct ?    13 Yes 6 No

what are the difference between protection class CT and Class PS CT..

Answer / manoj

Both Protection class and class PS CTs are used in
protection circuits only. As someone mentioned earlier,
class PS CTs are special CTs used in all types of
Differential Protetion scemes. they generally come in pairs
and they are special in sense their turns ratios,
impedances, VA burdens, knee point etc all these critical
parameters are exactly matched with each other.

Is This Answer Correct ?    8 Yes 1 No

what are the difference between protection class CT and Class PS CT..

Answer / satheesh

the saturation point between the ps is higher than
protection class & metering.and the accurracy is also
higher then protection CT. It has highly efficient so it is
mosly used in sofasticated protections (DIFF,DISTANCE )

Is This Answer Correct ?    4 Yes 1 No

what are the difference between protection class CT and Class PS CT..

Answer / mauhammad yasir abdul-rub

The Difference Between protection class and metering class
is mainly of saturation, the saturation values of protection
class is higher as when fault occur protection CT must not
get saturated as high current flows and metering CT can be
saturated as when fault occur metering is not necessary,
accuracy is also a factor but not the main factor

Is This Answer Correct ?    8 Yes 6 No

what are the difference between protection class CT and Class PS CT..

Answer / selvam.s

Protection CT:

this type of CT can be used for protect the breakers.

5P10,5P15 & 5P20 are called protection current transformer

1) 5 means accuracy of sensing fault current
2) 'P ' means "protection"
3) 10,15 & 20 means ( no.of times ( 10,15 &20 ) X actual
current rating of breakers .

PS CT:

PS means protection special current transformer.

this type CT can be used for differential protection in
transformer & in alternator.

Is This Answer Correct ?    2 Yes 0 No

what are the difference between protection class CT and Class PS CT..

Answer / r.suryamuthuraman

if any fault occurs core needs to saturated for protection
of ct.because ct secondary ckt will goes to relay current
coil .secondary ckt of ct will having resistance and
current.to avoid saturation want to decrease the burden of
ct.ps means special protection having high accuracy than
other class

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

In a simple spur gear train, gears with 24, 48, 32, 72 and 96 teeth are in sequence. The gear with 24 teeth runs at 900 rpm. The speed in rpm of gear with 72 teeth is

1 Answers   Caterpillar,


May I know how much values to be set for earth fault, over current and short circuit values at 11kv side? I have 11kv van 1250amps rating. Present it's taking load 80amps?

0 Answers  


How to check op amp using multimeter

1 Answers  


what is the maximim current drawn by 1 phase and three phase welding machine

0 Answers  


400 kvtransmission lines in india are connected in star or delta

10 Answers   NTPC,


3ph motor running with unequal kw and different pf what are the reasons

0 Answers   UltraTech,


how work the lighting arrestor?

2 Answers  


what is the thumb rule for determination resistance of resistor?

0 Answers   Siemens,


if its possible for step up or step down DC volage directly ? possible means how we can do it ?

5 Answers  


What is the use of 1:1 isolation t/f in any circuit...?

3 Answers  


what is the clearances between phease to phease & phease to earth in 400 kv transmission line?

1 Answers   Lanco,


phase colour is indicated by R Y B (red yellow blue) but in transformer i have seen U V W instead of (R Y B) have any meaning of this

3 Answers   Areva, Kim Yew,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)