how calculation to be done of cable size/o.h. conductor
size of 11kv h.t.for the load of 2175 kw
Answer / k.prakashchandra
The current is about 120 A. But it is not continuous.You
have to the study the list of OH conductors available in the
market.For 120 A and 50' Temp rise ,weasel ' ACSR conductor
is enough. Then you have to consider voltage regulation
which should not exceed 6% and further development. Rabbit
ACSR conductor is the next one with carrying capacity of 148
A for 30' temp rise and 183 A for 50 ' temp rise.Temp rise
is for calculation of maximum sag.
| Is This Answer Correct ? | 1 Yes | 0 No |
How many earthings are provided for a 250KVA distribution transformer?
What is the formula for finding fault level of generator?
How to calculate cable size between battery charger to Battery ?
working function importance of mdc meter
how to calculate the capacity of the AC motor
iam working in power plant. In hot places tube lights are glowing at the end portion only. what is the reason for that?
What are the conditions to be satisfied for parallel operation of dc generators?
How to convert KW to KVA or KVAR OR kvar/kva to kw?
Which type of power plant is more easier to produce electrical power at economical condition?
What types of testing in 11Kv Ht switchgeat during testing?
If a 3 phase induction motor is in off condition in the conveyor and rotor of the motor keeps moving with the conveyor than the resistance of windings of motor varies. why is it so ??
how we can improve P.F. by using capacitors ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)