how calculation to be done of cable size/o.h. conductor
size of 11kv h.t.for the load of 2175 kw
Answer / k.prakashchandra
The current is about 120 A. But it is not continuous.You
have to the study the list of OH conductors available in the
market.For 120 A and 50' Temp rise ,weasel ' ACSR conductor
is enough. Then you have to consider voltage regulation
which should not exceed 6% and further development. Rabbit
ACSR conductor is the next one with carrying capacity of 148
A for 30' temp rise and 183 A for 50 ' temp rise.Temp rise
is for calculation of maximum sag.
Is This Answer Correct ? | 1 Yes | 0 No |
whatis the test procedure for lightning arrester which was installed one year back. i want check it whether it is working or not.
what is earth pit , how we can measured it, what earth rods reference
Define availability (operational)?
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
what is softstarter?
Unbalance in voltages at motor terminals is caused by ____.
what is the effect if we add capacitor on DG supply, it has any loss or benefit.
we have one 75kw motor 380 volt 3ph amp134 please advise which size of cable required
while doing high voltage test on 11kv/433 distribution transformer why we only give 28 kv on hv side and 3kv on lv side for power transformers what is the value what factors it depends
how and where megger works?
what are the differance between neutral and earthing?