Answer / shipra
If it is perfectly earthed then there is no voltage
diffance between earth & neutral that means it will be Zero
in all condition.
| Is This Answer Correct ? | 461 Yes | 209 No |
Answer / suresh
voltage bw earth and nuetral is 100 to 200 milli volts if
it is perfect earthing
voltage b/w phase and earth is 230 volt for all phases
voltage b/w phase and neutral is varied from 220 to 230 v
it depends up on the phase balance conditions
| Is This Answer Correct ? | 303 Yes | 63 No |
Answer / vinod kumar
The Max and Minimum voltage between neutral - earth,
depands on type of earthing :-
if it is dedicated earthing and it is maintained properly,
the voltage between earth and neutral shall be 0 volt.
If it is a joint earth it may go to 1 to 2 volt.
| Is This Answer Correct ? | 219 Yes | 29 No |
Every electrical installations has earthings If it has
single earthing without joints
Neutral-earth-0 volts
with joints
Neutral-Earth= + or - 5volts
between phase-neutral
Phase-Earth=230volts
As per IEC,IEEE max voltage drop allowed in electrical any
installations should be below 2.5% of rated system voltage
| Is This Answer Correct ? | 147 Yes | 29 No |
Answer / ajit dalvi
Correct voltages are....
Pahse to Neutral 230
Neutral to erarthing 0
Earthing to phase 230
All other answers are wrong
| Is This Answer Correct ? | 172 Yes | 90 No |
Answer / saikrishna
generally the max. difference between voltage of neutral and
earth to be maintained is 3.5V.If it gets
crossed,circulating currents flow and equipment connected
gates damaged
| Is This Answer Correct ? | 103 Yes | 29 No |
Answer / sajad sharafudeen
In balanced condition the voltage between neutral and earth
is zero,if perfectly earthed.
There will develop voltage between neutral and earth in
propotianate with unbalanced condition.
| Is This Answer Correct ? | 90 Yes | 26 No |
Answer / pradeep
Regarding answer 11, i think in case the Neutral to Earth
voltage is high, it means there is an unbalanced load in
the three phases (in case of 3 phase supply) or the neutral
is not proper. Either way, there is a chance of current
flowing back into the circuit because of improper neutral
or earth not properly grounded, resulting in equipment burn-
outs in case of a surge. These equipments need not be
switched on and will burn-out in case of fault. Thus it is
recommended to keep the voltage between Neutral and earth
as low as possible.
| Is This Answer Correct ? | 43 Yes | 5 No |
Answer / ravindra sharma
The question can be replied in three conditions
When earthing is perfect and (a) neutral is solidly
earthed at transformer end then the volatge between erath &
neutral is zero and earth and phase is the same as between
earth & neutral in all conditions whether all pahases are
perfect or one of them faulty. and between earth and phase
is the same as neutral and earth i.e. nominal value when
system is healthy
(b) when neutral earthing is not solid but with resistance
then Voltage between neutral and earth will be zero in case
of balanced load on all three phases and it may rise max.
upto a value equal to phase value if there is fault on one
of the phase,depending upon the value of earthing
resistance of the neutral earthing. Value of earth to phase
will be nominal value if system is balanced and healthy,
and may go max upto phase to phase voltage if there is
fault on one of the phases and mind it again value in case
fault will depend on fault resistance.
In nut cell we can say that min. value between neutral and
earth will be zero volt and max. will be nominal voltage
(e.g 230 volt in indian LT supply case) and voltage between
neutral and phase will be nominal voltage is system is
balanced and healthy and mind it in case of fault it may go
down min. to zero value and max to phase to phase voltage!
and that is what great abt electrical enineering.
| Is This Answer Correct ? | 48 Yes | 22 No |
What is the unit of inertia constant of rotating machines? Which has more inertia constant between turboalternator and hydroaltermanor and why?
how we identify between current transformer and potential transformer without having it name plate?
why protection meter is always connect to star
the max. power will be transferred if …… a) sending end vol. is high b) receiving end v is high c)…….. d) corona loss is least
2 Answers Engineers India Limited,
what is surge suppressor?
what is MAR
why we avoid parallel operation of diesl generator?
if harmonics is generates on the secondary side of transformer then why we put LC ckt on prim side?(i m talking abt rectiformer transformer)
In both 600/1000 V cable and 450/750 V cable, we can supply 415 V. However for distribution, all utilities are using only 600/100 V instead of 450/750 V. What is the reason?
what is infinite in infinite bus
What are the disadvantages of LT AVR over HT AVR?
1 Answers APTransco, Jindal, TNEB Tamil Nadu Electricity Board,
why should small green grass ans small plant should not be there inside the transformer Yard in the factories
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)