What is min and max voltage between earth and neutral/phase
if it perfect earthing?
Answers were Sorted based on User's Feedback
Answer / shipra
If it is perfectly earthed then there is no voltage
diffance between earth & neutral that means it will be Zero
in all condition.
Is This Answer Correct ? | 461 Yes | 209 No |
Answer / suresh
voltage bw earth and nuetral is 100 to 200 milli volts if
it is perfect earthing
voltage b/w phase and earth is 230 volt for all phases
voltage b/w phase and neutral is varied from 220 to 230 v
it depends up on the phase balance conditions
Is This Answer Correct ? | 303 Yes | 63 No |
Answer / vinod kumar
The Max and Minimum voltage between neutral - earth,
depands on type of earthing :-
if it is dedicated earthing and it is maintained properly,
the voltage between earth and neutral shall be 0 volt.
If it is a joint earth it may go to 1 to 2 volt.
Is This Answer Correct ? | 219 Yes | 29 No |
Every electrical installations has earthings If it has
single earthing without joints
Neutral-earth-0 volts
with joints
Neutral-Earth= + or - 5volts
between phase-neutral
Phase-Earth=230volts
As per IEC,IEEE max voltage drop allowed in electrical any
installations should be below 2.5% of rated system voltage
Is This Answer Correct ? | 147 Yes | 29 No |
Answer / ajit dalvi
Correct voltages are....
Pahse to Neutral 230
Neutral to erarthing 0
Earthing to phase 230
All other answers are wrong
Is This Answer Correct ? | 172 Yes | 90 No |
Answer / saikrishna
generally the max. difference between voltage of neutral and
earth to be maintained is 3.5V.If it gets
crossed,circulating currents flow and equipment connected
gates damaged
Is This Answer Correct ? | 103 Yes | 29 No |
Answer / sajad sharafudeen
In balanced condition the voltage between neutral and earth
is zero,if perfectly earthed.
There will develop voltage between neutral and earth in
propotianate with unbalanced condition.
Is This Answer Correct ? | 90 Yes | 26 No |
Answer / pradeep
Regarding answer 11, i think in case the Neutral to Earth
voltage is high, it means there is an unbalanced load in
the three phases (in case of 3 phase supply) or the neutral
is not proper. Either way, there is a chance of current
flowing back into the circuit because of improper neutral
or earth not properly grounded, resulting in equipment burn-
outs in case of a surge. These equipments need not be
switched on and will burn-out in case of fault. Thus it is
recommended to keep the voltage between Neutral and earth
as low as possible.
Is This Answer Correct ? | 43 Yes | 5 No |
Answer / ravindra sharma
The question can be replied in three conditions
When earthing is perfect and (a) neutral is solidly
earthed at transformer end then the volatge between erath &
neutral is zero and earth and phase is the same as between
earth & neutral in all conditions whether all pahases are
perfect or one of them faulty. and between earth and phase
is the same as neutral and earth i.e. nominal value when
system is healthy
(b) when neutral earthing is not solid but with resistance
then Voltage between neutral and earth will be zero in case
of balanced load on all three phases and it may rise max.
upto a value equal to phase value if there is fault on one
of the phase,depending upon the value of earthing
resistance of the neutral earthing. Value of earth to phase
will be nominal value if system is balanced and healthy,
and may go max upto phase to phase voltage if there is
fault on one of the phases and mind it again value in case
fault will depend on fault resistance.
In nut cell we can say that min. value between neutral and
earth will be zero volt and max. will be nominal voltage
(e.g 230 volt in indian LT supply case) and voltage between
neutral and phase will be nominal voltage is system is
balanced and healthy and mind it in case of fault it may go
down min. to zero value and max to phase to phase voltage!
and that is what great abt electrical enineering.
Is This Answer Correct ? | 48 Yes | 22 No |
How reverse power relay sense the power is reverse in the system.
What will be result if we connect LT votage to the terminal of HT Transformer?
what is static excitation and dynamic excitation of synchronous generator,scr excitation is a brush or brushless excitation?
What is bode plot?
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
what is RTU with SCADA connection ?
i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?
in ct secondary one terminal is connected to earth why?
WHY R USE IN BRUSH IN THE MOTOR?
a solar energy installation utilizes a three phase bridge converter to feed energy into power system through a transformer of 400v/400v.the energy is collected in a bank of 400v battery and is connected to converter through a large filter choke of resistance 10ohms.1.the maximum current through the battrey will be.2.the kva rating of the input transformer is.
What is the basic of DTH.
what is the condition for YnD11