why we avoid parallel operation of diesl generator?
Answers were Sorted based on User's Feedback
Answer / goodwhisher
to lokesh
this site is very good for good engineers,please dont spoil
it please,it's no a funny matter.
dont answare if you dont know,please.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / johnson m.c.
1) Potential of both alternators must be equal. Both must
have same output voltage.
2) Phase sequences of both the alternators must be same.
The RYB phases of one alternator must
be connected the RYB phases of the other alternator.
3) Frequency of both the alternators must be equal. If one
alternator is operating at a frequency of 49
Hz and the other one is delivering voltage at 51 Hz, then
load on the second alternator would be
more. We have to increase the speed of the prime mover of
the first alternator in order to effect a
match in frequencies.
4) Phase angle of voltages of the two alternators must not
be more than 10 degrees.
5) During manual operation of synchronization, the load
could witness kick (which is a peak of
current). This kick could burn the alternators on the load.
The only solution is the use of automatic
synchronisation equipment. However, expert engineers could
close the CB of the second
alternator when the difference of phase angle between the
two voltages is 2 degrees.
6) The alternators must share loads with respect to their
ratings.
7) The alternators must have similar voltage drooping
characteristics.
8) The engines of the alternators must have similar
governor characteristics;
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / rajanikant
lokesh why you want to spoil this site this is very good
site for engineers
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / lokesh ranjith
because in parallel operation when electricity fails all Dg
sets will gets on even if the load is less also
There will be more diesel consumption
if we run the dgsetd solo mode we can give 80% load can get
goog efficiency
Is This Answer Correct ? | 2 Yes | 20 No |
What is MS-EXCELL?
In dc ckt. 24v or 110v, which one is more efficient and why?
During Millivolt drop test current leads are applied in the extreme ends and voltage leads are given just before the current leads.. what will be the difference if voltage leads are given in the extreme ends? and why?
we have one pumping station and 4.6 MW 7 no.s synchronous motors.so there is no required HT capacitor to improve power factor.But we have two no.s of 25 Mva power transformer connect to distribute the power for motors connect with 220 kv line.So i have required the HT capacitor to improve power factor at HT side i mean power transformer bus side.So please suggest how much HT capacitor banks required for same.
why capacitor bank shorted by resistance ( 3 terminal )
which starter is used for synchronous motor
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
What is the difference between Split ring and slip ring?
On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?
0 Answers TNEB Tamil Nadu Electricity Board,
what happened when we supply a dc current in dc motor?? can it worked properly?
How PADO software increase the efficiency of power plant?
can we load Power capicitors on DG sets?
14 Answers Neptune, Nimbus, Westin,