Answer / johnson m.c.
1) Potential of both alternators must be equal. Both must
have same output voltage.
2) Phase sequences of both the alternators must be same.
The RYB phases of one alternator must
be connected the RYB phases of the other alternator.
3) Frequency of both the alternators must be equal. If one
alternator is operating at a frequency of 49
Hz and the other one is delivering voltage at 51 Hz, then
load on the second alternator would be
more. We have to increase the speed of the prime mover of
the first alternator in order to effect a
match in frequencies.
4) Phase angle of voltages of the two alternators must not
be more than 10 degrees.
5) During manual operation of synchronization, the load
could witness kick (which is a peak of
current). This kick could burn the alternators on the load.
The only solution is the use of automatic
synchronisation equipment. However, expert engineers could
close the CB of the second
alternator when the difference of phase angle between the
two voltages is 2 degrees.
6) The alternators must share loads with respect to their
ratings.
7) The alternators must have similar voltage drooping
characteristics.
8) The engines of the alternators must have similar
governor characteristics;
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / rajanikant
lokesh why you want to spoil this site this is very good
site for engineers
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / lokesh ranjith
because in parallel operation when electricity fails all Dg
sets will gets on even if the load is less also
There will be more diesel consumption
if we run the dgsetd solo mode we can give 80% load can get
goog efficiency
| Is This Answer Correct ? | 2 Yes | 20 No |
what is a difference b/w earthing & neutral?
Make a list of materials and layout diagram for a 35hp motor, to be wired at 35meter away from the MDB in a chemical factory.
Actually why the transformers are rated in KVA.?
what is the power factor used by the PHCN in nigeria? 2. what is the difference between an alternator and generator. 3. Generation of poweris in KV but how is transmission is in MW. 4.If the transmission of power is 20,000MW how can it be increaesed to 80,000MW
Why can't we parallel Voltage transformer secondary circuits?
In transformers Which type of connection is preferred for harmonics to be minimum. primary : secondary star without neutral:open delta star with neutral :open delta star without neutral: delta star with neutral : delta explain why
For example, if I use Star delta transformer for distribution, Can I Connect 230 V lighting load bewteen secondary phase & primary neutarl. What will be the effect, if I connect in this manner?
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
what is dc mator?types of dc motor?losses in dc motor?what is the mechanical,electrical and commercial efficiency of a dc motor?
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
why motor range is available 22kv,30kv,37kv,45kv and so on? why motor range is not available 21kv,24,25,26,27kv and so on?
how to identify the cable quality and what is flame proof cable
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)