What is the unit of inertia constant of rotating machines?
Which has more inertia constant between turboalternator and
hydroaltermanor and why?
Answers were Sorted based on User's Feedback
Answer / iamdon
Inertia constant has unit of second(joule/VA).
Turboalternator has higher inertia constant in the range of
3-9 sec where as hydro alternator has inertia constant of 2
sec.
This variation is because in the case of turbo alternators
more then one(3 to 4) stages are connected to obtain high
mechanical input to alternator.Each stage has high rotating
mass.So more inertia constant.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 6 Yes | 7 No |
Answer / dwivedi sandeepdhar
kg_m^2
turbogenerator has more inertia constant because it rotate
at higher speed than hydrogenerator.
Is This Answer Correct ? | 3 Yes | 5 No |
what is intermediate switch
what happen when dc supply is given to the transformer
What is a formula to decide the size of the cable of the star delta motor ( From Contactor to the motor 2 runs )
what is transformer?
Explain why the Voltage drop will happen in 3 Phase line?
Why there are semi conductor layers on conductor and XLPE insulation of HT cables
The exciting current of a transformer is non sinusoidal. why?
if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with different % impedance will they be able to catter the load. what will be the ratio of load on the two transformers if the % impedance is in the ratio 1:2
what's the simultenous maximum demand (SMD)..what the diffrent MD and SMD?
What is the life of MCCB
If the line voltage is reduced to 75% of its rated value then by what percentage current will reduce ?? 75% 25% 50% no change and why ?
what are the difference between protection class CT and Class PS CT