What is min and max voltage between earth and neutral/phase
if it perfect earthing?
Answers were Sorted based on User's Feedback
Answer / deb
-Neutral-earth-0 volts(max. 5 volt)
-if Neutral-earth-1 volts, means perfect earthing(in a
office where load present.
At this condition neutral-phase voltage will bw higher than
earth-phase voltage. because leakage current pass through
neutral.
Normally neutral-phase voltage-220 +-10 and earth-phase
voltage same at no load condition(earthing 0 volt)
means if earthing in a office where equipment is running
and earthing voltage suppose 2 volt . the neutral-phase
voltage should be suppose to 220 volt and Earth-phase
voltage 218(neutral to phase voltage 220 volt-earth to
neutral voltage 2 volt = 218 volt).
Please currect me if i wrong
Is This Answer Correct ? | 29 Yes | 3 No |
Answer / samdipth
i think the difference will be between 1 to 3 volts.....and
the answer no 9 please let me know how come the equipments
will get damage if the difference will be above 3 volts?
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / muhammad khalid
earth to neutral voltage 0.1 to 0.9v.
100% perfect earth system.
any question plz call 03343262442
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / gopinath
Pahse to Neutral 230vac
Neutral to erarthing 0 to max 3vac
Earthing to phase 230vac
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / devendra kumar
440 volt three phase system
line to line 398.36 volt
phase to neutral voltage 230 volt
phase to earth voltage 230 volt
earth to neutral voltage 0 volt in single earthing without joints
and with joints Neutral-Earth= 0 to 5 volts
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / chandrakant rewatkar
min voltage is Zero ( if no joints)
max voltage is 3 volt ( if there is the joints)
if these value get in case of 3phase supply with P and N
if supply voltage is 415 without variation in voltage.
if value is more than 3 volts,
then load is unbalanced
Earthing not perfect
neutral not proper from incoming supply
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / shailesh singh
the voltagr between neutral and earth should lies between 0
to 5 vlts depending upon earthing arrangement.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / prasad das
The voltage differance between neutral and earth
will be zero,if it is perfectly earthed.
Is This Answer Correct ? | 5 Yes | 3 No |
define briefly the function of an ac electric generator (alternator)?
if sf6 gas low in gis what will happen
why low pressure side of the turbine is connected to the alternator and not the high pressure side??
Which motor has high Starting Torque and Staring current DC motor, Induction motor or Synchronous motor?
Can someone help me in the Below Quest on Earthing 1.Types of Earthing and Recommended for what use 2.What is the Pit value /Panel N -E value should be or within limit for RP and UPS .
WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,
1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf will indicate? 1.max pf it can supply 2.min pf it can supply like this 4 options there what is answer.explain
Just a silly question but just to make my curious mind bac to normal - Why was not 67 and 67N relays built into a single relay as i have noticed that the R,Y,B CT wiring end up into the 67 relay while the common of the R,Y,B CT wiring end up into the 67N relay. Then it was better if a single relay was manufactured just like the distance relay (21). Another question i would like to ask is - how do we know where the 67 and 67 N relay has to be placed.why is it not placed at the transformer bay? In the substaion that i am working -i have noticed that it is placed between a breaker and a common double bus bar and this line bay is connected to another substation at a remote place which is furthur connected to a load. B U S______CT for 67 & 67N ______Breaker _____ remot s/s. B A R
how to setting voltage RTCC panel
what is the relation between size of the anteena and wavelenghth of radiated wave
how a single machine can act as both motor and generator? and give explanation interms of connections?
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?