Answer / deb
-Neutral-earth-0 volts(max. 5 volt)
-if Neutral-earth-1 volts, means perfect earthing(in a
office where load present.
At this condition neutral-phase voltage will bw higher than
earth-phase voltage. because leakage current pass through
neutral.
Normally neutral-phase voltage-220 +-10 and earth-phase
voltage same at no load condition(earthing 0 volt)
means if earthing in a office where equipment is running
and earthing voltage suppose 2 volt . the neutral-phase
voltage should be suppose to 220 volt and Earth-phase
voltage 218(neutral to phase voltage 220 volt-earth to
neutral voltage 2 volt = 218 volt).
Please currect me if i wrong
| Is This Answer Correct ? | 29 Yes | 3 No |
Answer / samdipth
i think the difference will be between 1 to 3 volts.....and
the answer no 9 please let me know how come the equipments
will get damage if the difference will be above 3 volts?
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / muhammad khalid
earth to neutral voltage 0.1 to 0.9v.
100% perfect earth system.
any question plz call 03343262442
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / gopinath
Pahse to Neutral 230vac
Neutral to erarthing 0 to max 3vac
Earthing to phase 230vac
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / devendra kumar
440 volt three phase system
line to line 398.36 volt
phase to neutral voltage 230 volt
phase to earth voltage 230 volt
earth to neutral voltage 0 volt in single earthing without joints
and with joints Neutral-Earth= 0 to 5 volts
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / chandrakant rewatkar
min voltage is Zero ( if no joints)
max voltage is 3 volt ( if there is the joints)
if these value get in case of 3phase supply with P and N
if supply voltage is 415 without variation in voltage.
if value is more than 3 volts,
then load is unbalanced
Earthing not perfect
neutral not proper from incoming supply
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / shailesh singh
the voltagr between neutral and earth should lies between 0
to 5 vlts depending upon earthing arrangement.
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / prasad das
The voltage differance between neutral and earth
will be zero,if it is perfectly earthed.
| Is This Answer Correct ? | 5 Yes | 3 No |
what is meaning of AMF, WHY IS USING IN GENSET
Does power factor vary with speed?If yes, how?If not, why?
What is the main purpose of c.f.b.c.boiler
explain single phase series motor
WHAT IS THE MEANING CREEPAGE DISTANCE
HOW TO DRAW THE VECTOR DIAGRAMS OF A Dyn 11,YdN 1 transformers?
what will happen if we give a dc supply to a transformer.?
can any one suggest me the tilt angle of my solar pannel ?? or tell me how can i know the fix tilt angle of my solar pannel?? my cordinates are 31.503629,72.993164.
should Dy11 and Dy1 group can be operated in parallel??????
what happens if dc supply is given to the transformer?
in science exhibition how lamp can blink when you clap near the lamp ? thank you
Can you please explain creepage distance in detail, for a 6.6kV cable head what must the distance be and how do you determine it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)