In split range control, we will control 2 outputs with time
interval. Eg :(with 4-20 ma signal, for 4-12 ma we are
operating one control instrument like valve & for 12-20ma we
are operating other control instrumet (other valve). If we
get a signal of 15ma to first instrument (Valve 1), what
will happened to the first valve, and if we get signal above
20 ma to 2 valve what will happened ?
Answers were Sorted based on User's Feedback
Answer / kyle condran
It depends on the setup the 2 above post both correct the following scenario can also be seen sometimes.
Valve 1 set for 4-12mA (100% open @ 4mA and 0% open at 12mA)
Valve 2 set for 12-20mA(100% open @ 20mA and 0% open at 12mA)
For example if you have a temperature control with 2 valves one controlling steam and one controlling chilled water, going into a heat exchange process, when we want to increase temp out of heat exhanger contol signal goes up towards 20mA chilled water valve closes and steam valve opens. when we want to cool the process down the opposite happens and the control signal falls towards 4mA the steam closes and chilled water valve opens.
so 4mA is full on chilled water 20mA is full on steam 12mA is both closed.
lets assume fail open cooling / fail closed heating valve.
as for 15mA on valve 1 depending on where the split range is done, ie controller or valve.
for our example if done in valve it will ignore anything above 12mA and be fully closed.
above 20mA in our example will be ignored by valve 2 since it is allready at 100% at 20mA.
see http://www.contek-systems.co.uk/Documents/split_range_control.htm for the first 2 post
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / romeo
The first valve will open fully open (100%) and the second
valve will open at about 37.5% only.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pramod suwalka
1. at 15 ma signal first Valve open fully.
2. at 20 ma signal Both Valve open fully.
| Is This Answer Correct ? | 1 Yes | 5 No |
As an industrial instrument technician what we have to know?
How will you calibrate an interface level trol/normal level trol in line and in w/s?
what is the main supply source for pressure transmitter?
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar
I need circuit for RTD senser?
What is the three element? And how it work?
1)why we are using mostly Ultrasonic Flow meters to measure flow, rather than Radar waves? 2)why we are using Ultrasonic waves and Radar waves to measure the Level?
How to convertion 100 m3/hr to mmH2O or to Kg/cm2?
Which is the best field foundation bus. ( FF ) Yokogawa, Honeywell or others ?
What is furnace draft control?
what is meant by turn down ratio?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)