In split range control, we will control 2 outputs with time
interval. Eg :(with 4-20 ma signal, for 4-12 ma we are
operating one control instrument like valve & for 12-20ma we
are operating other control instrumet (other valve). If we
get a signal of 15ma to first instrument (Valve 1), what
will happened to the first valve, and if we get signal above
20 ma to 2 valve what will happened ?
Answers were Sorted based on User's Feedback
Answer / kyle condran
It depends on the setup the 2 above post both correct the following scenario can also be seen sometimes.
Valve 1 set for 4-12mA (100% open @ 4mA and 0% open at 12mA)
Valve 2 set for 12-20mA(100% open @ 20mA and 0% open at 12mA)
For example if you have a temperature control with 2 valves one controlling steam and one controlling chilled water, going into a heat exchange process, when we want to increase temp out of heat exhanger contol signal goes up towards 20mA chilled water valve closes and steam valve opens. when we want to cool the process down the opposite happens and the control signal falls towards 4mA the steam closes and chilled water valve opens.
so 4mA is full on chilled water 20mA is full on steam 12mA is both closed.
lets assume fail open cooling / fail closed heating valve.
as for 15mA on valve 1 depending on where the split range is done, ie controller or valve.
for our example if done in valve it will ignore anything above 12mA and be fully closed.
above 20mA in our example will be ignored by valve 2 since it is allready at 100% at 20mA.
see http://www.contek-systems.co.uk/Documents/split_range_control.htm for the first 2 post
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / romeo
The first valve will open fully open (100%) and the second
valve will open at about 37.5% only.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pramod suwalka
1. at 15 ma signal first Valve open fully.
2. at 20 ma signal Both Valve open fully.
| Is This Answer Correct ? | 1 Yes | 5 No |
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
why we are maintain the gap voltage in vibration probe when installing time can explain me?
what is AWG?
what is dc moter.
0 Answers Jindal Steel and Power, Lupin,
WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
23 Answers Exxon Mobil, Honeywell,
give me all the details about the interview and which type of question being asked
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.
if field commnictor 475 does not communicate with transmitter what will you do ?
Steve said that "An eddy-current probe works by passing an alternating current through a coil of wire and measuring the coil’s impedance" while we are using -24 Volt DC , So I am confused about DC and AC. Plz .
2 Answers Jindal, Sadara Chemicals,
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
why we use only 4 to 20ma other than 0 to 16 ma
How many types of sensors are used in instrumentation & what are names
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)