In split range control, we will control 2 outputs with time
interval. Eg :(with 4-20 ma signal, for 4-12 ma we are
operating one control instrument like valve & for 12-20ma we
are operating other control instrumet (other valve). If we
get a signal of 15ma to first instrument (Valve 1), what
will happened to the first valve, and if we get signal above
20 ma to 2 valve what will happened ?
Answer Posted / romeo
The first valve will open fully open (100%) and the second
valve will open at about 37.5% only.
Is This Answer Correct ? | 1 Yes | 2 No |
Post New Answer View All Answers
Which type of pressure can be measured by primary elements?
What is modbus?
whats the abbreviation of IOP? is it instrument of power or input open problem?
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
what is the PC interface and software for connection to ABB logic module “ LM011-CE18RAC “ ( for Programming ) ??
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
what is difference between HOT permit and cold permit
What is Cavitation in a control valve?
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
I want to measure and control level in tank of size 10*5 filled with gasoline, so plz give me the solution with clear details. how to select transmitter and sensors.
Why boiler chimney area oxyden sensor fixing?
What is the difference bitween control net scaner and device net scaner
1. For Steam drum level signal, why do we compensate with drum pressure signal? 2.For main steam Flow signal is comensated with main steam temperature signal and main steam pressure signal why?
plz tell me clearly about PID.."when v have to change I value,D value,GAIN??
Working principle of magnetic flow meter ......and calibration procedure of e+h magnetic flowmeter...