why we use only 4 to 20ma other than 0 to 16 ma
Answers were Sorted based on User's Feedback
Answer / vimal
Whether our instrument is in good condition or not, in order
to check that we are using 4ma as a low value. If we use 0
ma, We can't say that whether the problem is in instrument
or in supply panel.Normally, when we not give supply to the
instrument it will show 0 ma. for that, we use 4 ma as a low
value. Moreover we use 4 to 20 ma as a standard output
because to get linear graph. So, we prefer 4 to 20 ma
instead of 0 to 16 ma..
| Is This Answer Correct ? | 33 Yes | 2 No |
Please give you attention below:
4 mA 0 %
8 mA 25 %
12 mA 50 %
16 mA 75 %
20 mA 100 %
at the time of no voltage (zero voltage) we get 0 mA
at the time of 24v dc supply we get 4 mA.
IF we keep the range starting from 0 mA we will get 0 mA at
the time of zero voltage & 24 V dc voltage supply which is
technically not good.
If your observation is too good that time you will
find that from above every gap between each other of 'mA'
& '%' the differrences are equally same.
see for mA : 0-4-8-12-16-20 (gap of 4 mA equally)
and see for % : 0-25-50-75-100 (gap of 25 % equally)
This things easily helpful to sort out the problems.
Therfore this STANDARDISATION is Universal.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / faiyaz ahmad
4 to 20 mA is a analog signal and its continuous signal its allow to 1 to 5 volts in this signal because its drop of voltage its not drop of current that's why its called standard signal its electrical out put of the transmitter.
4 mA is zero
20 mA is hundred
| Is This Answer Correct ? | 0 Yes | 0 No |
Because we want to check the tx is damaged or not.If it
will be normal & no process variable applied then we can
get o/p 4mA...if it will damaged then o/p will not show 4
or near about..
| Is This Answer Correct ? | 5 Yes | 7 No |
Answer / sandeep varma
the instruments starts responding from 4mA
| Is This Answer Correct ? | 0 Yes | 13 No |
what is easiest way to read STL language in PLC?
what is piezoelectric transducer?give an example in power plant n state its principle?
What is cold junction compensation in thermocouples? How is it achieved?
the whole paper was based on Transducers..questions like define repeatability, error,accuracy,precision..den there were many q. on the conversion of Pa to mmHg and other units.. also..der wer few Q. on some level sensors(with diagram)
how can we measure the pressure in underground cooling water pipeline by using pressure transmitter?what about the tapping position?
components of control circuit belongs to control valve
The DCS has the following signal type:
HOW TO DO PERFECT CALIBRATION OF DIFFERENTIAL PRESSURE TRANSMITTER FOR CLOSE VESSEL TANK LEVEL PURPOSE ???? AND HOW TO MAKE ZERO PRESSURE ?? Rosemount 2051 Pressure Transmitter with HART® Revision 5 and 7 Selectable Protocol BIENG USED !! HOW TO CALIBRATE FIELD SIDE DPT WITH THE HELP OF SPAN & ZERO PUSH BUTTONS ??
Explain the working principle of lvdt?
Draw a great bridge circuit.
for oil & gas industries which zone is normally preferred? why? give its example?
where can we use viberation transmitter,and how can we control viberation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)