Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.
Answer / carl_ellis
The RTD element is ALWAYS isolated from the sheath. Dual
element RTDs should be isolated from each other.
Therefore, there should be no common electrical connection
between any wire in a dual element RTD.
The fact that a connection to one receiver (the PLC)
disturbs the other receiver's RTD reading means either
a) the RTD elements or lead wires are shorting to either
the sheath, the other RTD element or a lead wire; meaning
the RTD assembly is damaged internally.
b) the field wiring for one RTD is shorting to the field
wiring of the other RTD
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between conductive lined pipe and conductive unlined pipe? Why do we see that?
0 Answers Process Control Technologies,
Explain pH, Conductivity.
What is ALSPA 370 control system
1 Answers DUBAL-Dubai Aluminium,
what does a positioner in control valve ?
IF PLC POWER FAILURE THEN WHAT HAPPEN?
selection of the zener barrier for the hazardeous area zone 0
What is T4 temperature in compressor?
please explain about actuator action? direct action & return action ?
Why capacitive banks ar5e important?
In Safe Guarding test what means by "Failed to Danger" ?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
Why flow/pressure transmitter before control valve?