Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.
Answer / carl_ellis
The RTD element is ALWAYS isolated from the sheath. Dual
element RTDs should be isolated from each other.
Therefore, there should be no common electrical connection
between any wire in a dual element RTD.
The fact that a connection to one receiver (the PLC)
disturbs the other receiver's RTD reading means either
a) the RTD elements or lead wires are shorting to either
the sheath, the other RTD element or a lead wire; meaning
the RTD assembly is damaged internally.
b) the field wiring for one RTD is shorting to the field
wiring of the other RTD
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between intrinsic instruments and ATEX instruments?
two common seiling liquid used in seal pots are:
Anybody can tell me how to convert mmHg2o /psi to scfm please give me formula of conversion
what are the standards used for earthing instruments in the field?
How can we check Zero of DP type Level Transmitter onside?
What is the difference between a Extension cable and a copnesating cable.Where can we use compensating cable. Is anywhere compensating cable are used for mv transmission to the indicator.
can we create an interrupt in plc through scada?
what is the use of impulse line in AFBC boiler , WHY WE CONNECT IMPULSE LINE TO TRANSMITTER , DRFT GAUGE ETC ????????
1.what is beta in control valves? 2.what is the condition followed by light in LASERs? 3.1kg/cm2=?psi 4.Integral action reduces what? 5.about vena contracta 6.a simple RC circuit 7.thermistor material's temp coefficient of resistance 8.if wave passes through the thicker area of a chord to a thinner area what changes will occur to wavelength? 9.if 4-20 mA represents 0-10 kg/cm2 what will be the current when pressure is 5 kg/cm2.................
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?
what is the role of proportional in process control?
Calibration of flow transmitter.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)