if field commnictor 475 does not communicate with transmitter
what will you do ?
Answers were Sorted based on User's Feedback
Answer / mallu byali
We have to conform before connecting the hart communicator
into tx whether it is smart family or not if may other then
connect the resistance series into the its terminal do the
calibrate.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / carl_ellis
1) Check for 24Vdc? Yes, but assuming the power supply is
24Vdc, don't expect the voltmeter to read 24v, unless you're
back in the control panel where the power supply is.
If you're out in the field where the transmitter is, you are
not close to the (-) side of the power supply, so where do
you put the black voltmeter probe? The only place for it
on the transmitter's (-) terminal, but measuring voltage
across the transmitter's (+) and (-) terminals only shows
what the transmitter's voltage drop is, not what the source
voltage is.
There is the voltage drop across all parts of the loop, the
transmitter, the load and the wiring. So checking voltage
across the transmitter's (+) and (-) terminals will never
show a full 24Vdc because of the voltage drops in the loop.
With short wiring runs and a 250 ohm load resistor, the
voltage across the (+) and (-) transmitter terminals might
be as high as 23V @ 4.0mA output, but could be as low as 10V
with a 20mA output across 500 ohms.
2) Checking to confirm that the transmitter is a smart
transmitter is a good idea. There are protocols other than
HART or Foundation Fieldbus (Honeywell's DE), and there are
lots of 'dumb' transmitters, too.
Some brands, like Siemens, allow HART to be enabled or
disabled, so the transmitter may be HART capable but have
the HART comm disabled.
3) Connecting a resistor in series is a good idea if the
load resistor is an unknown.
The article at the link below tells why a HART loop needs at
least 230 ohms of resistance
http://blog.lesman.com/2011/10/06/add250-ohm-resistors-to-make-hart-work/#more-68
The temporary use of a 250 ohm resistor is typical because
they're so common in a process plant.
4) Is the HART device at address 0 (zero)? The
communicator can talk to any address, but when connecting
point-to-point on home run wired transmitters, the
expectation is that the transmitter will be at HART address 0.
5) Experience will show that there are the inevitable
problems like
- broken or corroded communicator leads or clips that can go
'open' or be intermittent.
- power supply ripple or EMF induced noise on the loop
circuit can conflict with HART's 1200 baud FSk digital
communications
- some loop device, like a loop isolator or HART-unfriendly
loop indicator has stripped off the HART signal with a low
pass filter, leaving only the 4-20mA current signal
- wrong version DD so the communicator will connect but only
perform the so-called "common commands".
Tell 'em Carl sent you.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abu maryam
In my opinion there are several causes of this problem:
1- Check the power source if it 24 volt or not.
You should disassemble the power source if it is 24 on out side and still 24 after connecting to device this mean that the power source is good but if it is 24 volt out side and zero after connecting this mean there is found problem in power source (may be problem in module).
2-Read device data if it support hart protocol or not.
3-Disassembled device and connect separate power source and connect 250 ohm series if it no benefit added change the resistance from 250 to 1000 ohm and try or disassemble the resistance and power source and apply power source from multi function calibrator which has internal resistance then try to connect.
4-May be device support hart but hart property is disabled by definite internal jumper in device so we should change this jumper according to device manual.
5-May the device support hart its data files is not added to hart communicator for 1 of the following 2 reasons:
the first:hart communicator is not updated.
The second:the device data filed is not added to hart communicator and it need its special programs and its special cable as found in foxporo transmitters.
6-May the connectors or cables has problem so use another cable.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / marut_tripathi
first check 24 vdc power have or not in transmitter.
termination proper or not of transmitter.
| Is This Answer Correct ? | 1 Yes | 2 No |
Why we use 250 ohm resistor in series with HART protocol communication?
13 Answers Chemtrols, Instec, Sabic,
what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..
why we go for pcbs
what is difference between DO and DI
what is the electrical operation procedure for switching on 27.6MVA electric furnace.
How to Calibrate variable Head flowmeter (Orifice), here we dont know High pressure and low pressure then how to apply pressure on HP and LP side ?
What is SLPC & MLPC? How it works?
I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
HI THIS IS NOOR AHMMAD.SHAIK, I AM WORKING IN INSTRUMENTATION MAINTENANCE Dept. in BOILER HOSE(BHEL HYDERABAD),,any other persons are working in same dept. i want some HELP in my subject
Can any one send me IOCL instrumentation question papers.. i dont know the pattern of the questions and what to prepare can any one help me on this .. my email id is anwarnishil@gmail.com
WHAT IS THIS INSTRUMENTATION?
what is the procedure of O2 analyser calibration?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)