Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why three wire is using with a RTD?

Answers were Sorted based on User's Feedback



Why three wire is using with a RTD?..

Answer / guest

Resistanc Temperature Detector(RTD)encorporates two basic
concepts

1)Variation of temperature varies the resistance of Pt wire.
2)Variation in resistance affects the balancing of DC
bridge circuit.

For measurement purposes lead wires are brought out to make
external connections.These lead wires have some resistances
which affects the bridge balancing.

Since we can not reduces the resistances of lead wire to
zero.So, either 3 wire or 4 wire connection is employed to
ELIMINATES THE IMBALANCING TO THE BRIDGE CIRCUIT caused by
resistances of lead wires so that an accurate measurement
can be made.These wires(3 or 4) are called compensating
leads.

Author:arbelectbit@yahoo.com

Is This Answer Correct ?    29 Yes 4 No

Why three wire is using with a RTD?..

Answer / sam

You are right, and the temperature indication does not
increase so significantly that it is worth the effort to use
a 3 or 4 wire RTD.
It might increase with something like 0,001Deg C so that is
so small you might as well say there is no difference in the
accuracy of a 2,3 and 4 wire RTD, using a local or smart
transmitter.
In the old days we use to use a 2 wire RTD in the field and
then run a cable say 200m to the temperature indicator. By
the time it gets to the indicator the temperature is
completely different from what it was in the field due to
the cable resistance that add itself the the RTD resistance.
We compensated for that by installing a 3de wire for the
sole propose to measure the resistance of the cable itself
and deduct that from the total resistance measured at the
temperature indicator.
So the actual resistance of the RTD as measured at the
temperature indicator is RTD - RLine1.(or [(Rline1/2)x2]if
you want)
With the 4 wire it makes it more accurate in that you can
now measure line one and line 2. The theory is that the one
line might have a small difference compare to the other line.
So the actual RTD resistance at the temperature indicator is
measured RTD - [(RLine1/2)+(RLine2/2)]
But since we all use the small compact local and smart
temperature transmitters these days, 3 and 4 wires are no
longer needed since the distance from the RTD to the
transmitter is only from about 50 to 500mm and but it seems
it have stayed due to some design engineer always saying,
why buy a 2 wire if you can get the 3 and 4 wire for just
about the same price. It will make the indication just more
accurate, but they never say by how much (0,001Deg C)
Good luck

Is This Answer Correct ?    14 Yes 0 No

Why three wire is using with a RTD?..

Answer / maswood alam

Actuly there is little diffrence b/w 3 wire nd 4wire, 3wire
has 95% accurcy nd 4 wire has 100% but 4 wire more costly nd
both are use as long distance so we genarally prefared 3
wired RTD System......

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?

4 Answers  


What is the purpose of LO Overhead tank in turbines.

0 Answers   ADMA OPCO,


what is plc? Basic function of plc? application of plc in industry? What is lader diagram ? What is the main advantage to use plc in industry?

15 Answers   Schlumberger,


why we are using boosters at glass furnace is there any other thing?

1 Answers   CGL,


what can of fault ofently come in vibration mesurement?

0 Answers  


How does milli volt is created in themocouple?

2 Answers   Jaypee,


How to make position transmitter feedback reverse i.e at valve close i want 20ma output and at full open 4ma.for the NELES positioner,model:ND8261/TS1.

3 Answers  


warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?

1 Answers  


What is possitive and negative feedback?

3 Answers   KNPC,


how will do square root transmitter calibration

2 Answers   Roche,


Why Current(Ampere) is chosen as Fundamental Quanties not Charge(coulomb) ?

3 Answers  


What is the purpose of the analyzer in petrochemical plant?

0 Answers   ENI, Lakshmi Machine Works,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)