which type signal come control valve
Answers were Sorted based on User's Feedback
Answer / mani
from dcs we give 4 to 20 ma to i/p converter. from i/p we give the 3 to 15 psi pnematic signal given to cv.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bert
The type of signal going to control valve is either a
pneumatic or electronic signal. For a pneumatic signal its
3 to 15 PSI or 0.2 to 1.0 kg/cm2. For electronic signal its
4 to 20 mA.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / abdulbasit137@hotmail.com
two types signal come control valve 1.pneumatic signal 3 to
15 psi (2)electronic analog signal 4 to 2o milla amp
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / parag pathak
Control Valve is final control element of clost loop. So
signal coming to control valve will be in pneumatic form
but depends on size of Valve. It can be 3-15 PSI or 0.2 -
1kg/cm2 but it is not fixed. There is one instrument called
Positioner which will convert 3-15 PSI signal to desired
siganl depending on Control valve.
For any Contol Valve signal will come from Control room in
the form of 4-20 mA. this 4-20 mA signal was converted to 3-
15 PSI signal by instrument called I/P converter. This
siganl will go to positioner and the positioner o/p is
given to valve actuator to get desired opening and closing.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajkumar.diice
The signal type depends on
the location of control valve!
For explosive hazard area the
signal be pneumatic and be 3
to 15psi! The converters be
mounted in somewhat
distanted area! For all control
valves the signal be 4to 20mA
over 1to 5 volts from a
control room! For inbuild
current to pressure
converters control valves the
signal be 4to20mA over 1to
5volts dc
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / susant
from dcs analog output signal 4-20ma dc provided to control
valve
| Is This Answer Correct ? | 3 Yes | 6 No |
What are the Components of Siemens S7 300 Series PLC system ?
Pressure tx shows 1 mbar but we need 1000 mbar at this process condition .. how can we sort it out .
how to calibrate TT transmitter
can any one help me to get bel probational engineers sample question papers. I have applied for it.
how many parts of valve positioner?
Explain Three way boiler.
what are the on/off valve precaution?
How to Calibrate Flow Switch in field
What means zero and span in transmitter callibration.
What happen if I install my pressure transmitter below the elevation of pipe in natural gas service?
What is the difference between uv and ir scanners? and what is the workig principle of both
What is mean by analytical instrumentation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)