Please anyone answer my question, what is the difference
between single acting and double acting control valve, in
what condition we better choose single acting rather than
double acting
Answers were Sorted based on User's Feedback
Normally a control valve is refer to by it's fail position.
This means "what position will the valve move to should the
supply air or control signal to the valve falls away". This
is important to safe guard the process at various places so
some valves will be fail open and some fail close. In order
to have valve as a fail open or close the valve the actuator
have to be spring loaded. So by having the spring on top or
bottom of the actuator piston, will determine if it will be
a FO or FC valve. This kind of valve is also called single
action since it will only have one output from its
positioner to either the top or bottom of the actuator. The
positioner on the valve is also setup as a single acting
positioner since it will only give a single action to the
actuator, the reverse action will be done by the spring. The
problem with this setup is that it is possible that the
process might be so strong or the pressure so high (during a
blow down or ESD shutdown in the plant) that the spring
might in certain instances be to week to push the valve into
the fail position quick enough, due to the back pressure
from the process and can cause damage to the plant or even a
explosion. To make sure that the valve will go to the fail
position we install a double action positioner with two
outputs. One goes to the top of the actuator and one to the
bottom. This is also very helpful to do very accurate and
stable control on a high flow line since the pressure from
the position do the actual control and not spring control
one way and positioner control the other way as in single
acting control valves. It is also solving the problem that
the valve will now be forced into the fail position by the
spring as well as the positioner supply pressure during a
emergency.
In shutdown valves (open/close ESDV's) the same is true and
sometime at critical and high pressure points we use
hydraulics instead of pneumatics as the double acting agent
to make sure the valve will close during a emergency.
So to summarize the double acting action in ESD and control
valve is just there to make sure the valve will do what it
was designed for. Call it a extra fail safe if you want. In
theory not needed since a single acting valve should do the
trick just as well,but in practice you are at time very glad
you did it especially if you look at the kind of pressures
the valves are working on. With those kind of flows and
pressures you don't want to leave anything to chance.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / b.c.bhatt
Basically single acting valves returns to their original
position as the control input goes off. These can have NO
or NC positions depending upon the application .In double
acting valves or bistable valves ,the position is retained
even when control input is withdrawn.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is piezo electric transducer?its principle?
what is the difference between plant earth and instrument earth? and what type of cable( cable size ) used for both? and why ?
what is preventive maintenance , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
What happen if I install my pressure transmitter below the elevation of pipe in natural gas service?
the 3 most common transmitter protocol being in refinery or qatar gas and aramco.
Generally in which location ( JB or IO card or DCS) the thermocouple compensation is done.Also where they measure the atmosphere temp ( for compensation) in JB OR DCS panel? How they compensating that atmosphere temp? is any circuit for that ( like in rtd wheatstone bridge)?
we want to control pump in let pressure and tank (for exp) our inlet line if water cam and pump will on and when our tank will full pump will off also if our inlet pressure low pump will off even tank not full.this pump i want to uses on our water supply line.
What is input and output of vaiberation transmitter and what is its unit.
what's the criteria of using over range protector when installing Pressure Gauge
Explain ratio control system.
I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width
What are the interlocks we have to check during the start up of LP/HP compressor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)