HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO
Allen-Bradley SLC500



HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO Allen-Bradley SLC500..

Answer / carl_ellis

The 3300 is a 2 wire, loop powered guided wave radar level instrument. So it needs 16-42Vdc for power; typically a 24Vdc power supply is used. Copper wire cable, shielded, twisted pair is used. If the radar is in a hazardous area, then either the installation is designed for explosion proofing or Intrinsic Safety (which uses a barrier or I/S isolator).

The SLC500 PLC needs a 4-20mA current analog input card. Usually the instrument power supply is separate from the rack power supply.

The wiring is shown in the manual, but it is traditional 2 wire loop powered wiring.

Carl Ellis
Measure First

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe

0 Answers  


What is the difference between a double acting and single acting positioner? what type of valves use single acting positioners?

1 Answers   AquaTech, NamPower, Samson Resources,


Why Differential pressure transmitter is located below the tappings points for steam & condensible vapor flow measurement application?

2 Answers  


What is Process portal A(PPA)?

1 Answers   ABB,


Explain bernoulli’s theorem.

0 Answers  






What are the two states of a controller

3 Answers  


How to measure density of oil in your kitchen. i.e indirectly to verify the quality of oil using min. gadgets available in the kitchen/house.

1 Answers   HPCL,


How a rtd work, and what volts/current goes to a RTD to measure the resistence?

1 Answers   DVC,


SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?

4 Answers  


Can anyone convert a 5/2 way or 3/2 way valve into an ISO valve?

0 Answers  


How to calibrate Toxic gas detector?

0 Answers   Supertech,


what is the main supply source for pressure transmitter?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)