HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO
Allen-Bradley SLC500
The 3300 is a 2 wire, loop powered guided wave radar level instrument. So it needs 16-42Vdc for power; typically a 24Vdc power supply is used. Copper wire cable, shielded, twisted pair is used. If the radar is in a hazardous area, then either the installation is designed for explosion proofing or Intrinsic Safety (which uses a barrier or I/S isolator).
The SLC500 PLC needs a 4-20mA current analog input card. Usually the instrument power supply is separate from the rack power supply.
The wiring is shown in the manual, but it is traditional 2 wire loop powered wiring.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 1 No |
What is SLPC & MLPC? How it works?
how to calculate the total flow in square root
how to rectify the poor signal strength in utrasonic digtial flow meter ,model:ge digital xce868i
i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?
why we use 4-20 mA for calibration of the instruments.why we cant use 0-20 mA?
how to measure flow with dp
If a normal magnetic type flow transmitter that can measure flow, temperature and show this parameters on field, is it possible by any means to get this (flow and temperature) parameters info. On dcs? And if yes then with HART, FO communication or any other communication system?
1 Answers Process Control Technologies,
what is moisture probe? What are there types? What is there working principle and how they works? guys this is one of technical question I had ask in interview. If you know its answer please let me know. The interviewers were more interested in microwave moisture probe, so if you find its any link please just forward me on my mail id.avinash1200@gmail.com Thanks in advance.
how to work MIL contol valve posistioner ?
I want to measure bidirectional steam flow? Kindly suggest me a suitable flow meter. steam is superheated at 41kg/cm2, 350°C
what is cold loop? difference between hot and cold loop?
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)