The 3300 is a 2 wire, loop powered guided wave radar level instrument. So it needs 16-42Vdc for power; typically a 24Vdc power supply is used. Copper wire cable, shielded, twisted pair is used. If the radar is in a hazardous area, then either the installation is designed for explosion proofing or Intrinsic Safety (which uses a barrier or I/S isolator).
The SLC500 PLC needs a 4-20mA current analog input card. Usually the instrument power supply is separate from the rack power supply.
The wiring is shown in the manual, but it is traditional 2 wire loop powered wiring.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 1 No |
A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe
What is the difference between a double acting and single acting positioner? what type of valves use single acting positioners?
1 Answers AquaTech, NamPower, Samson Resources,
Why Differential pressure transmitter is located below the tappings points for steam & condensible vapor flow measurement application?
What is Process portal A(PPA)?
Explain bernoulli’s theorem.
What are the two states of a controller
How to measure density of oil in your kitchen. i.e indirectly to verify the quality of oil using min. gadgets available in the kitchen/house.
How a rtd work, and what volts/current goes to a RTD to measure the resistence?
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
Can anyone convert a 5/2 way or 3/2 way valve into an ISO valve?
How to calibrate Toxic gas detector?
what is the main supply source for pressure transmitter?