howmuch current can carry the 2.5Sqmm copper cable?

Answers were Sorted based on User's Feedback



howmuch current can carry the 2.5Sqmm copper cable?..

Answer / harit

Actually Current carrying capacity is depends upon, upto
which length your cable runs.

Is This Answer Correct ?    124 Yes 48 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / vijay khilnani

Dear Sripellirajukumar
I had answered 7 Amps and mentioned the thumb rule for
copper is 2000 Amps per sqaure Inch ( not 2000 Amps per sq
mm ) > You need to read the answer carefully before
commenting . For Your info 1 sq inch = 25.4 x 25.4 = 645 sq
mm. Also copper purity / type of insulation / temperature
rise allowed / voltage drop tolerarable would be other
factors which need to be considered. For this 2000 Amps / Sq
inch has a generous margin ie it is has some safety margin .
Vijay Khilnani

Is This Answer Correct ?    71 Yes 17 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / jokemaster

its the cable to carry the current and not the current to
carry the cable.:-)

Is This Answer Correct ?    38 Yes 16 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / ayad basha

The general thump rule is one square inch copper conductor
will carry 1000 Amps and that of for aluminium conductor is
600 Amps. So, for Cu, 1sqmm = 1.6 Amps appx. and for Al 1
sqmm = 0.9 Amps.

but this will not fit for the increasing cable sizez.

for example for 400Sqmm cable, it will not carry 400 x 1.6=
640 Amps. That is the effective current density of the
conductor decreases as the conductor size increase.

Also depth of cable laying, ambient temperature and cable
grouping also should be considered.

Is This Answer Correct ?    29 Yes 17 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / sripellirajukumar

ya mr vijay khilani ur answer might be correct but first u
have to mention the thumbrule ..instead of that u said rule
in ur first question..ok ur answer might be correct...

Is This Answer Correct ?    13 Yes 3 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / him

Around 15 Amp if cooling is natural . Thumbrule 6 Amp per
Sqmm

Is This Answer Correct ?    10 Yes 8 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / ravi pandey

it can carry current upto 16-20 amp

Is This Answer Correct ?    6 Yes 4 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / s.m murshed monowar

2.5 sqmm cu cable which voltage drop /mm is 9.7 ,it will
carry 16 amps maximum distance 30 meter & it will carry 20
amps for maximum distance 25 meter

Is This Answer Correct ?    2 Yes 0 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / golak

Standard: 20A

Is This Answer Correct ?    18 Yes 17 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / npatra

It depends for which you are using.
1. Inside wall it's maximum capacity defined is 16Amp.
2. For Equipment its's Maximum Capacity defined to be 25Amp

Is This Answer Correct ?    4 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Does the isolator has a making capacity????????

2 Answers  


WHAT IS NORMAL VECTOR GROUP USED FOR DESIGNING OF TRANSFORMERS??

11 Answers  


How do we calculate over and under frequency tolerance from generator data?

0 Answers   DPS,


A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?

2 Answers  


Why stand-by earth fault relay and restricted earth fault relays are connected between neutral and ground in transformer?

1 Answers  






how i can calculate the size for fire cable

0 Answers   Adani Power,


What is meaning of star delta connection / delta star connection and which one is best and what is the advantage?

0 Answers  


When alarm is activated in buccholz relay in transformer

1 Answers  


what is the current law ?

4 Answers   Aster, TCS,


Explain the Term in CT Name Plate – Class: 5P10

6 Answers   Jindal, SRES,


what is difference b/w HT & LT and the range of HT & LT ?

22 Answers   AF, Schneider,


I want to merge a cable..in between two metering Cubicals which contains CT's and PT's and Energy meter..before taking merger..what are the common things required?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)