Answer / vilas
2.5 sq.mm copper cable cable can carry the current safely
as per following, however it depends on the length.and
isulation of the cable ,i.e. voltage levels ,for extra
length increase the size.
Up to 20 meters.
1) for single phase,230 volts, 29 amps.,two and three core
cable
2) for three phase 440 volts system 24 qamps. four core
cable, with neutral
| Is This Answer Correct ? | 8 Yes | 15 No |
Answer / krishna
2.5 Sqmm cable can with stand upto 25 Amps Pratically. But
how you are calculating please explain it to me clearly.
Still I am confused.
| Is This Answer Correct ? | 10 Yes | 19 No |
Answer / shaun
The answer also depends on the time for which the wire is
carrying the curent.... is it pulsed condition or,
continuous condition....
| Is This Answer Correct ? | 4 Yes | 17 No |
Answer / subalsaha
:-actually 2.5 sq. mm cable can carry 3amp ie(1.5x2)=3Amp
| Is This Answer Correct ? | 5 Yes | 21 No |
Answer / manjunath
Hi am Manjunath
2.5sqmm cable carry max14.8amps
| Is This Answer Correct ? | 4 Yes | 22 No |
Answer / vijay khilnani
7A but depending on wire length voltage will drop : rule is
2000Amps can be carried by 1 sq inch of copper
| Is This Answer Correct ? | 44 Yes | 66 No |
Answer / sripellirajukumar
hi this is rajkumar ....
actually every 1sqmm wire can carry 3ams of current ....
so for 2.5 sqmm it will be 2.5*3=7.5amps
thanks...
| Is This Answer Correct ? | 47 Yes | 74 No |
Answer / sripellirajukumar
Vijay Khilnanis answer is dead wrong...1square mm wire can
not carry 2000amps man....thnk before u answer ok na..if u
donot know dont answer..ok na
may be my answer is correct..as explained above
| Is This Answer Correct ? | 18 Yes | 52 No |
What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing?
why does make gain margin and phase margin on same plot.?
Technical specification of a wind farm
what should be 3phase motor capacity or rating to connect in star connection. what should be 3phase motor capacity or rating to connect in delta connection. what should be 3phase motor capacity or rating to connect in star delta connection
why we are using DC violtage for testing of cables....which is used in HV AC applicatons...
please tell me when we start motor without load in star or delta connection whose current above condition,pl write formula
Befor synchronissation of Generator what test to be carried out.pl.specify with reason.
working principle of UPS
why they were using TRIAC instead relay in some controllers and what is the advantages.
What is NDR in HT capacitor panels.
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
What is the advantangeous over SFU (switch fuse Unit) & FsU (Fuse Switch unit) which one is better & application of Both?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)