Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


howmuch current can carry the 2.5Sqmm copper cable?

Answers were Sorted based on User's Feedback



howmuch current can carry the 2.5Sqmm copper cable?..

Answer / siva shankar

THE CURRENT CARRYING CAPACITY OF 2.5 SQMM IS 22A.IT IS A STANDARD FOLLOW BY CABLE COMPANY AND IT ALSO DEPEND WHICH MATERIAL USED BY U FOR CONDUCTING.

Is This Answer Correct ?    4 Yes 3 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / bobcat_rob_ oman

For NEC 25 amps depending on waht kind, thW, THHN, TW PVC
IEC 23 amps

better see manufacturer's ampacity... this is the required
ampacity at normal ambient temperature 30degree celsius.

Now if you will installing this to a certain area... then
you must consider the correction factors such as ambient
temerature, distance of installation, type installation(
grouping factor, wall cavity installation, direct burial,
etc..) then you apply these correction factors.. and there!
you have the proper ampacity for a 2.5 sq. mm copper
wire....

Is This Answer Correct ?    3 Yes 2 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / vinay patel

It can carry current up to max. 22 Amps. at 20 De.Celsius
temperature with copper cable DC resistance 7.98 Ohm/Km.
with 0.7 mm PVC insulation as pe IS:694/1990

Is This Answer Correct ?    1 Yes 0 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / ajay goel

Hi I am Ajay Goel....
As thumb rule every 1 sqmm wire can carry 3 Amps of Max
current during transmission Hence 2.5 sqmm will carry 7.5Amps.
However for chassis wiring it can support 32 Amps.

..AJAY GOEL

Is This Answer Correct ?    1 Yes 0 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / phanikanth

it is cabble to carry 1kv=4am so 2.5sqmm carry in 8.2am

Is This Answer Correct ?    2 Yes 1 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / harish

10amp

Is This Answer Correct ?    1 Yes 0 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / francis

it a gatefull if I get answer thank u

Is This Answer Correct ?    1 Yes 0 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / sennapparajan

Max 10 amps as per standard.

Is This Answer Correct ?    13 Yes 13 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / ajay dhari

The 2.5 Sq.mm Copper cable can practicaly carry current 22
Amp but theortically is it mentioned 25 Amp by
manufacturers which is tested by ERDA.

Is This Answer Correct ?    19 Yes 19 No

howmuch current can carry the 2.5Sqmm copper cable?..

Answer / sandeep arora

For me its surprising to see such an contradictory
calculations
Practically in automotives, we calculate 10Amps = 1 sqmm
& approx 22A for 2.5 sqmm in DC(12/24V)

Could any body elaborate for this contradictions?

Is This Answer Correct ?    4 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

In LRS how much water PH value maintain for good operation of motor?

3 Answers  


simple way to find busbar sizes??

1 Answers   SPAC,


purpose of flux relay for turbo generator in power plant

1 Answers  


what is the chiller and working principal

0 Answers   Blue Star,


What is the Power factor of DC Power system ?

9 Answers  


How to protect a Dosing pumps/any sensitive equipment (single phase) from surge protection inside a food factory.

0 Answers  


How i measured Bus bars weight without wighting ?

3 Answers   Encom,


In power generator sets, when they are coverted from 50hz to 60hz, the kva rating after conversion increases. For example, the manufacturer of a perkins 200kva @ 50Hz generator set has mentioned it to become 220kva after converstion to 60hz. What is the relation between the frequency & the KVA rating. Any formula please.

3 Answers  


What is trip and closing coil in cb? Why need of them

0 Answers  


What is the material used for the core of a high freiquency transformer?

3 Answers   Videocon,


what is the basic differnce between ground and earth

3 Answers  


If I have a motor of 1MW with 6.6kv, running at 35% load, how can i save energy without reducing the load ?

2 Answers   Reddy Labs,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)