for a 11kv transmission line what capacity of CTs & PTs are
required?
Answers were Sorted based on User's Feedback
Answer / srinivasan.s
For 11KV line CT ratio was 1200A-600A-300A/1Amp
PT ratio was 11KV/110V
for 11KV CT's PT's minimum 3cores are available
generally 1'st core for metering
2nd and 3rd cores for protection purpose.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / khalid k usafzai
for installing cts and pts on 11 kv line first of all the load to be connected is required.then we will proceed.bye
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / shivadathathri
11 KV CTs & PTs , Out door Pedestal mounting versions will do. Current ratio , STC Rating & Insulation level can be determined with connected load. Like breaker / Transformer Etc. Example : Load is 11KV 100KVA transformer is connected . Then use 11KV Cts CTR: 5/5 Amps , Class 0.5 for metering , Class : 5p10 for Protection . OCF - 150XI nominal . Oil cooled CTs for MUSS. If it is mounted inside panel / Control room then Use Resin cast type. SHIVADATHATHRI- 9632153842.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / alternate_reality
A 100/5 Amp CTPT can be installed for metering purpose in
Indsustries...
| Is This Answer Correct ? | 2 Yes | 3 No |
I got shortlisted in RRB thiruvananthapuram for the post of Junior Electrical engineer, waiting List - 7. i want to know about the validity of the current list and chance to get the job please help anybody knws abt it,, thank you
what is the principle of operation of synchronous motor and generator? explain in detail.
why the supply power frequency is 50hz in india? where as it is 60hz in US?
what is the maximum current rating in india for home?
identify the components of the tube light and explain how they function???wat is inside the fluroscent tube???how it works???
A transformer is used to light a 24volts,70watts lamp from a 240a.c main.The current in the main cable is 0.35A. Calculate, (1) The efficiency of the transformer. (2) the current in the lamp.
when we decide to use soft starter drive or vfd drive in mcc to operate apump?
Why an ac solenoid valve attract the plunger even though we interchanges the terminal? Will the poles changes?
FLP zone Types and Details
In an electrical power supply,why if neutral phase of a 3phase supply fail over current occur but if it's single phase supply neutral phase fail low current occur?
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply
How to measure current and voltage in an ELV circuit
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)