HOW MANY EARTHINGS REQUIRED FOR GENERATER
Answers were Sorted based on User's Feedback
Two eathing are req. minimum. Since the star point is
earthing solidly, and obviously the generator frame/housing
also to be provided with earthing to prevent any shock due
to insulation failiure.
if the generator is connected with a fuel tank, (for higher
size), it is necessary that, fuel tank to be grounted to
prevent lightning surges and any static voltage generations.
| Is This Answer Correct ? | 28 Yes | 5 No |
Answer / sudheer siddani
depends on the rating of the generator upto 125kVA two
earthings is sufficient one is neutral and one for
body.>125kVA four erthins are required two for neutral and
two for body
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rajeshsan
The earthing of Generator at star point is depends on the capacity.
For larger generators eg:- 600MW generator the generator is grounded using NGT and generator body is grounded at two ends. Earthing are done at two ends to have redundancy only.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pankaj singh
there should be two earthing required.one for star point
and another for body. At the star point there should be a
solid grounding,on the other hand body frame should be
earth diagonally and the material for grounding depend on
the rated valtage of generator
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / ajay kumar das
Normally minimum 4 earthing required .2 for body earth & 2 for neutral,But in case for 11 KV generation another 2 earth is required for L.A.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bhasker reddy
Depends on the KVA rating of generator earthing are required.
less than 40 kva atlest 2 earthing(one neutral & one body earth). more than 40 KVA 4 earthing (2 neutral & 2 body earth). if KVA rating increased should increase earthing.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gunasekaran
their are two system earthing at single voltage level in
generation one is generator neutral another one is PT
earthing and body earthing also provided
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nagaraj u.n
2.( body or frame) earthing should be used.because in case
of 1st point is faild ,2nd point is worked .it safety for
generator & opperatore.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / kiran patil
Only one at the star point of generator which should be
solidly grounded
| Is This Answer Correct ? | 5 Yes | 14 No |
what is the formula of high voltage testing of three phase induction motor?
When one of three series resistors is removed from a circuit and the circuit is reconnected, the current
63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?
why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is function. i am going to instal a 5oo kva tranformer & 380 kva DG set what should the earthing value
8 Answers Altrion Technologies,
Keywords: Die, Card, Coin, B/N 2 To 12
What should be the BDV value of a new transformer oil
Why does the phase voltage of two healthy phases become equal to the line voltage in case of an ungrounded neutral 3 phase star connected sytem when a single line to ground fault occurs ?
How is operate breaker failure scheme in substation
what is meant by dielectirc medium? what is the dielectirc value of air and water???
1.what is the reason for transformer and lightning arrester blast in 33kv system
what is ISF
We have a distribution transformer of 750KVA/11kv/440v and an AVR (Servo Stabilizer) of 750KVA on the LT side of distribution transformer. Also we have an ACB of 1200A on the output of distribution transformer (that is on the input of AVR). We want to have an MCCB on the output of AVR. What should be the rating?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)