HOW MANY EARTHINGS REQUIRED FOR GENERATER
Answers were Sorted based on User's Feedback
Two eathing are req. minimum. Since the star point is
earthing solidly, and obviously the generator frame/housing
also to be provided with earthing to prevent any shock due
to insulation failiure.
if the generator is connected with a fuel tank, (for higher
size), it is necessary that, fuel tank to be grounted to
prevent lightning surges and any static voltage generations.
| Is This Answer Correct ? | 28 Yes | 5 No |
Answer / sudheer siddani
depends on the rating of the generator upto 125kVA two
earthings is sufficient one is neutral and one for
body.>125kVA four erthins are required two for neutral and
two for body
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rajeshsan
The earthing of Generator at star point is depends on the capacity.
For larger generators eg:- 600MW generator the generator is grounded using NGT and generator body is grounded at two ends. Earthing are done at two ends to have redundancy only.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pankaj singh
there should be two earthing required.one for star point
and another for body. At the star point there should be a
solid grounding,on the other hand body frame should be
earth diagonally and the material for grounding depend on
the rated valtage of generator
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / ajay kumar das
Normally minimum 4 earthing required .2 for body earth & 2 for neutral,But in case for 11 KV generation another 2 earth is required for L.A.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bhasker reddy
Depends on the KVA rating of generator earthing are required.
less than 40 kva atlest 2 earthing(one neutral & one body earth). more than 40 KVA 4 earthing (2 neutral & 2 body earth). if KVA rating increased should increase earthing.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gunasekaran
their are two system earthing at single voltage level in
generation one is generator neutral another one is PT
earthing and body earthing also provided
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nagaraj u.n
2.( body or frame) earthing should be used.because in case
of 1st point is faild ,2nd point is worked .it safety for
generator & opperatore.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / kiran patil
Only one at the star point of generator which should be
solidly grounded
| Is This Answer Correct ? | 5 Yes | 14 No |
how to work droop ct in generating station
Office , overtime and television how big this stage?
What types domain of laplace transforms? What behavior can laplace transform predict how the system work?
There are Two questions about Steam Turbine Generator... What is HRSG bypass of LP, HP used for in power generation? In particualar, in the event that fault of HP bypass, there would be STG TRIP in operation but none on the LP bypass fault...what's the reason ?
what is PI value and its significance for insulation testing?
Why sometime AVR and sometime Booster coil is used in Alternator? what is the diferance between AVR & Booster coil due to which they are selected
how vector surge relay works ?
what are the values to be accepted on 3 core 185sq mm for 11000volts on insulation resistance between conductors and between conductors and earthed?
why transformer fuse wire is very thin as compared to home fuse wire while voltage lavel is low
Draw the DOL starter and star delta starter drawing?
what is means of CLASS in current transformer name plate?
can anyone help me regarding bout Electrical designs and calculations .. which text book should i follow as i am a trainee engineer.Description of my work which is Electrical designs like cable sizing, lighting, lightning, Gensets sizing, motor sizing, transformer sizing, generator sizing, circuit breakers, PDB MCC PCC SLDB MLDB panels, Single line diagrams mainly, substation desings, cable routing and layouts, reactive power compensations, power factor improvement, voltage drop calculations, power generations, power transmission, power distributions all calculations.Please help me
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)