HOW MANY EARTHINGS REQUIRED FOR GENERATER
Answers were Sorted based on User's Feedback
Two eathing are req. minimum. Since the star point is
earthing solidly, and obviously the generator frame/housing
also to be provided with earthing to prevent any shock due
to insulation failiure.
if the generator is connected with a fuel tank, (for higher
size), it is necessary that, fuel tank to be grounted to
prevent lightning surges and any static voltage generations.
| Is This Answer Correct ? | 28 Yes | 5 No |
Answer / sudheer siddani
depends on the rating of the generator upto 125kVA two
earthings is sufficient one is neutral and one for
body.>125kVA four erthins are required two for neutral and
two for body
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rajeshsan
The earthing of Generator at star point is depends on the capacity.
For larger generators eg:- 600MW generator the generator is grounded using NGT and generator body is grounded at two ends. Earthing are done at two ends to have redundancy only.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pankaj singh
there should be two earthing required.one for star point
and another for body. At the star point there should be a
solid grounding,on the other hand body frame should be
earth diagonally and the material for grounding depend on
the rated valtage of generator
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / ajay kumar das
Normally minimum 4 earthing required .2 for body earth & 2 for neutral,But in case for 11 KV generation another 2 earth is required for L.A.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bhasker reddy
Depends on the KVA rating of generator earthing are required.
less than 40 kva atlest 2 earthing(one neutral & one body earth). more than 40 KVA 4 earthing (2 neutral & 2 body earth). if KVA rating increased should increase earthing.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gunasekaran
their are two system earthing at single voltage level in
generation one is generator neutral another one is PT
earthing and body earthing also provided
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nagaraj u.n
2.( body or frame) earthing should be used.because in case
of 1st point is faild ,2nd point is worked .it safety for
generator & opperatore.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / kiran patil
Only one at the star point of generator which should be
solidly grounded
| Is This Answer Correct ? | 5 Yes | 14 No |
I have 1500KVA transformer ,How much Maximum KW Load is allowed?
15 Answers GKC Projects Limited GKCPL,
Why Cables are always circular and not square or rectangular?
what effect on electrical equipment if PF is gone over 0.996 in leading when provider say that its keep in minimum 0.996lagging
If I need to purchase a step-down transformer (from three phase 33kV 50Hz to 400/230V), what additional information do I need from the main supply power line?
How to identify the whether its an isolator or Breaker in MDB
Whata are the types of Cables?
what is the reason for indication of light in the earth lamps of main switchboard.if there is an earth why does one lamp get dim and the other two bright.
how many types of ct retio
what is the transformer rush current?
IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL. AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE PROVIDED
pre arcing time of ehv breaker
Why control of DC motor is simpler?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)