IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT
CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL.
AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE
PROVIDED
Answers were Sorted based on User's Feedback
Answer / sudhakar g
First you have to caluclate the load of the T/F i.e
KW=KVA*p.f
KW=500*0.8=400KW
I=kw*1000/1.732*415v*0.8
I=696.74 A
Based on these we can choose the Cable size ....
suppose the LT AL cable of 3.5c x 400 sqmm will give 530 A
of polycab....if we go for two runs of 400sq.mm means it is
good and the breaker size we will go for 800A ACB bresker
means it is good....
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 17 Yes | 13 No |
best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?
Is Indian railway uses 25000v ac or dc?
can we load Power capicitors on DG sets?
14 Answers Neptune, Nimbus, Westin,
what will happen if synchronous machine rotor fed from single phase ac supply
We have one Energy meter for Measuring the voltage,current,power,energy(KWH,KVARH,KVAH) & power factor.The problem is that the meter does not show whether the PF is lagging or leading.So i want to know that is there any way or calculation to find out that whether the PF sign (lagging or leading) depending upon the above mentioned parameters?
What is the acceptable resistance range of UPS battery
how the inner and outer body is separated in aircrafts?
How much water ( Kilo Liters) a submercible pump of 35 HP can lift from Borewell of 6" and 900 feet dip.
what is mean by marshalling box in transformer?
what could be the RMS value and average value of a 4 phase sine wave?
What happens to the synchronous generator when reverse power is given to it?
Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)