Answer / sudhakar g
First you have to caluclate the load of the T/F i.e
KW=KVA*p.f
KW=500*0.8=400KW
I=kw*1000/1.732*415v*0.8
I=696.74 A
Based on these we can choose the Cable size ....
suppose the LT AL cable of 3.5c x 400 sqmm will give 530 A
of polycab....if we go for two runs of 400sq.mm means it is
good and the breaker size we will go for 800A ACB bresker
means it is good....
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 17 Yes | 13 No |
what are the duties of commutator in motor and generator?
what is the reason for earthing static equipments? why?
How will you Protect aeroplanes and Ships from Lightining?
While converting delta into star or star into delta ,the three values of resistances remains unchanged .Find out the value?Let In star R1=x;r2=x;R3=x On converting into delta,R12=x;R23=x;R31=x Find the value of x
what is the difference between power transformer & distribution transformer and what are their ratings respectively?
How cmd is calculated in case of energy neters
Can i get some examples of mechanical devices?
Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?
what is the difference between synchronous & asynchronous generators
How to know th details about an electrical Drawing ? Please mention the easy method.
how to calculate Amp, 2 different Amp of batteries? Example: No. of Batteries = 2 Battery voltage = 12V 1st Battery rating = 17AH 2nd battery rating = 30AH between parallel connection then output volt 12v Amp?
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)