How to identify the whether its an isolator or Breaker in
MDB
Answers were Sorted based on User's Feedback
Answer / suresh
an isolator on or off doing by manualy but breaker tripps
autometicaly depend on trip setting
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / shri..
Breaker has trip function, breaker can operate
automatically like opening & closing the circuit with help
of UV & CC coil. It case over current it will trip.
Isolator has no trip function it has fuse. in this case we
can open & close the circuit by manually. It case over
current fuse will open.
Is This Answer Correct ? | 9 Yes | 1 No |
these all above are differences only but to identify ,read
details printed on device
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / sunil parmar
circuit breaker only opens only when there is a fault
condition or fault current or abnormal conditions is sensed
by CT via protecting relay via CB --(opens)
after then the isolator is opened manually or automatically.
but at the time of maintenance or future expansion in the
line the isolator is opened first followed by breaker and
then the charge within the lines are discharged then the
maintenance work is carried out..........
for any disagreement reply me on parmar20072008@yahoo.com
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.p.sharma
BE CLEAR THAT ISOLATOR HAS NO FUSE MEANS IT HAS NO
PROTECTION IT IS ONLY A SWITCH.
Is This Answer Correct ? | 3 Yes | 1 No |
what is power factor
I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.
I want formula to calculate cable size as per load given in length & amp. I searched many sites but didn't right answer. Please reply me asap.
What is partial discharge in power cable?
I have motor of 3 H.P. How i found the rating of capacitor use in it in single phase motor..???
why autotransformers are not safe for supplying low voltage from a high voltage source?
I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?
What should be cable size for 75KVA 380/220 3ph transformer
what is lowest system voltage?
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
difference between isolator and circuit breaker?????
what is surge arresters ?........