I have 1500KVA transformer ,How much Maximum KW Load is
allowed?
Answers were Sorted based on User's Feedback
In distribution system, generally the p.f. taken in account
is 0.8. So the maximum kw load available is 1500x0.8=1200kw.
For safest condition the diversity factor should be taken
into account is 80%. So the maximum 960kw (80% of 1200kw) of
load is allowed on a 1500KVA transformer.
| Is This Answer Correct ? | 115 Yes | 6 No |
Answer / ashutosh + mukesh
In distribution system, generally the p.f. taken in account
is 0.8
Beacuse our transformer is 1500KVA.
SO = 0.8
FROM FORMULA:- KW = KVA*P.F.
so KW = 1500*0.8
KW = 1200
So our transformer upto 100% load= 1200KW
Beacuse we take maximum 80% load on Transformer for safety
so: =1200* 80/100
=960kw
| Is This Answer Correct ? | 61 Yes | 7 No |
Answer / pardeep
actually first of all we calculate the load and after that
we would be able to slect the transformer. ok any how if
you have 1500kva transformer you can take 1200kw to 1350 kw.
its depends upon the dversity factor. how much you will
take.i know only this answer if anybody else has some other
please correct me.
| Is This Answer Correct ? | 42 Yes | 15 No |
Dear,
Transformers are designed for p.f. 0.8
Even if you make your power factor unity (which may sometime
disturb your source), you can not load transformer up to
100% of its capacity. It will raise threat to your costly
machines. Being good engineer, you should not let your
consumer exceed loading your transformer more than 90 % that
becomes 1350 kW (if p.f. is unity) and 1100kw (if p.f. is 0.8).
Regards
| Is This Answer Correct ? | 37 Yes | 11 No |
Answer / sayed asef
Dear its very simple
first just convert this 1500 KVA into KW at assumin PF 0.8
which equal to 1200 KW then Calculate the Ampere by the
Below Formula
P = 1.73 X V x I X PF
then you will get the Ampere,and then you can easily find
out the load by ammeter or any how you know abt 1200KW.
so you can put the load 1200 KW but being good engineer
dont put 100 % load on your transformer ,its better if you
put 80 or 90 % load.
thanks
regds
sayed asef s ali
| Is This Answer Correct ? | 27 Yes | 4 No |
Answer / sai seddy
In transformer, the current in line with voltage,so here
there is no cosine angle between the voltage and
current.but Practically some angle present in the voltage
and current.so the power factor should be more than 0.9.
KVA = 1500
P.F = 0.9
KW = 1500*09
=1350KW.
For Safe working allowable = 80% of rated of rated voltage.
Safest power = 1350*0.8
= 1080 KW
| Is This Answer Correct ? | 27 Yes | 13 No |
Answer / walid
IF PF=1
Max KW=KVA=1500
IF PF < 1
kw < kva ( <1500)
| Is This Answer Correct ? | 21 Yes | 10 No |
Answer / usha chandel
From the given transformer ,the max. power we can take
depend on the load p.f which we connect with the
tranaformer.As the pf has max value of 1,so at unity pf we
can take 1500 Kw from this transformer or the max power
from the transformer we can take is 1500 Kw
| Is This Answer Correct ? | 37 Yes | 28 No |
Answer / jun domdom
The answer will depend on the load itself.
Practically, they used 80% once you get the power by obtaining the process done as the number one answer above, it is correct.
But considering the entire load is diffrent.
You have to consider the losses, harmonic, heat etc.
But in my previous experience I thought it will shut down when I reached the 80% maximum load out of open delta 75kva transformer. My current reading is 265A and still increasing.
I'm waiting for shut down and burn of the transformer,
But it does not happen.
I reached even 455A and my heart is about to burst rather than the transformer.
So therefore transformer can withstand the maximum load up to 133% or even more.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / anton
Most transformers are at there best efficiency at 90 - 100% load therefore if you are being billed for your energy use on the HV side you don't want to have a transformer way to big and lightly loaded, most transformers will handle 100% overloads for short periods without dropping there output voltage, supply authorities would rather see a transformer intermittently overloaded than way oversized and massive losses when not very loaded, the reduction in lifespan from intermittent overloading is well and truly paid for in savings of the losses a larger transformer would have over its life
| Is This Answer Correct ? | 0 Yes | 0 No |
In AC Drives How can change & control its output Frequency?
Specify the crystal frequency required for an 8085 system to operate at 1.1MHz
transformers? power factor? machiences?
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
mccb service sittings be done?
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???
two transformers of the same type, using the same grade of iron and conducting material, are designed to work at same flux and current densities, but the linear dimension of one are two times of the other in all respects. The ration of kVA of the two transformer closely equal to................? options: 16, 8, 4, 2
If the positive terminal of batteries in 125 v dc system is connected to earth what will happen ?
which surface is suitable for NEUTRAL GROUNDING ?
How much load with stand the copper cable by sq mm apro..
what is the cost of a analog tachometer, for lab purpose/
what is rms value?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)