If I need to purchase a step-down transformer (from three
phase 33kV 50Hz to 400/230V), what additional information do
I need from the main supply power line?
Answer / subra
Operating voltage primary = 33KV
operating voltage secondary= 400v/230v
capacity of the transformer=?
tap changer =Online or off line
transformer oil cooling sys ONAN or ONAF
vector group=?
Indoor or oudoor tranformer
these are the details to collected
Is This Answer Correct ? | 7 Yes | 0 No |
what will happen if we pass a dc current through a ac bulb of 60 watt.The dc current is half ac one
phase clearance between phase to phase and earth
What are the reason of unbalanced secondary voltage of HT transformer 33kv/6.6kv ? Incomming voltage is balanced.33kv each secondary voltage 6.6 kv 6.4 kv 6.4 kv At no load conditions.
why current flows from +ve to -ve terminal
What is hipot test procedure?
Why should not we run the IM in low voltage, if runs means what will happen?(for example instead of 400V we give 250V supply)
Why we say three phase voltage 440v.
before transformer oil dielectric strenght tests are taken the oil should be allowed to settle to remove option 1 air bubbles 2 gasses 3 contamination 4 water
what happens when one of the phases out 0f 3 phases been removed under working condition and no load condition will the machine run if so plz send me why
How Negative Phase Sequence Relay works in case of Synchronous Motor?
how does a tube light starter works?
What range of speed can you get with the armature control method of speed control of d.c. Shunt motor?