Answer / shonali
there is no CW and CCW synchronization it depends on the
speed difference
synchronization is connecting our generator to grid by
matching with the grid frequency.
a synchroscope is used if our generator speed is less than
grid speed (frequency) the synchroscope rotates counter
clock wise (lag).
if our speed is high the scope needle rotates CW (lead)
if it is equal the needle stops
| Is This Answer Correct ? | 21 Yes | 6 No |
Answer / jock
To ensure the incoming generator takes up load as soon as
the generator circuit breaker is closed.
If synchronism was achieved with the synchroscope
indicating an anti-clockwise rotation the generator would
not take up load and instead would driven by the bus, ie.
reverse powered. If the reverse power is large enough
tripping of the generator is likely to occur.
When manually synchronising a generator to the bus it is
normal to give a quick 'increase' command on the controls
just after the breaker closes to ensure positive power
loading takes place.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / amritpal singh sidhu
I think this is due to the phase sequence, because we use
the sine wave in electrical generation so the sine wave
produced is according to quadrants(In which sine wave is
plotted CLOCKWISE ).
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / vikas wadhwa
In my point of view; in modern turbo-generators there is
already provision of about 5% automatic load command as
soon as gen. breaker is closed thus leaving no chances of
gen. tripping on reverse power. Hence, it will not make any
difference technically whether syncronization is done in
cloclwise or anticloclwise direction.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / anees ur rehman
I hope that answer 2 and 4 are v.good.Normally
synchronisation done at 1/10 frequency of incoming
generator kept higher thans the exisisting source.why.yes
when it is synchronised as generator take load its speed
decreases due to low frequency it will trip so its
frequency is kept 1/10 times more than source
| Is This Answer Correct ? | 5 Yes | 3 No |
Synchronization should be done in CW direction , to avoid reverse power trip , because CW means your alternator speed and voltage is slight greater then grid ,after immediate synchronizing load will delivered to grid , other wise there is change of reverse power trip.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheena mahany
i didnt get anything . be a little bit more clear....
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manav
There are five conditions that must be met before the
synchronization process takes place. The source (generator
or sub-network) must have equal
line voltage, frequency, phase sequence, phase angle, and
waveform to that of the system to which it is being
synchronized.
(source:----wikipedia)
Clockwise mode of operation is a standard.It has been set to
ensure that phase sequence is not reversed while
synchronizing the generators. Otherwise, same thing might
happen as explained in Answer #7.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mukul
synchronisation is done in CW direction coz generator should have voltage slightly more than tha system .. because at tha time of synch system start taking load from generator instantly. to avoid generator speed lower than the rated one this needs to do.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.anandsah
It doesn't matter if you synchronise TG with Grid in cw or anti cw . Just after synchronisation increase the power as soon as possible.
| Is This Answer Correct ? | 0 Yes | 0 No |
why need of ac exietation in alternater.
An input device is interfaced with Intel 8085A microprocessor as memory mapped I/O.The address of the device is 2500H.In order to input data from the device to accumulator,the sequence of instruction will be
FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER DIFFERENTIAL PROTECTION DOES NOT OPERATE???
what are factors to be consider in electrical installation like load factor,diversity factor .....
How is operate breaker failure scheme in substation
Size of the power cable like 1.5,2.5,4 sq.mm which area calculated from whick area or how specified the size?
Why we should use delta connection in primary and star connection in an distribution transformer, which converts 400v a.c. voltage to 33kv.
15 Answers ABC, Kirloskar, Sify,
What is the basic difference between directional and non directional over current protection?
In induction machine when the load increase the current will increase .why? what is the relation ship between the sleep and current drown by stater?
why transformer do not rotate?
What is meant by harmonic distortion?
7. A resistance of 30 ohm is connected across 240v supply. If a resistance R ohm is connected in parallel with 30ohm resistor across the same supply, the current drawn becomes triple of original one The unknown resistor R is
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)