Answer / shonali
there is no CW and CCW synchronization it depends on the
speed difference
synchronization is connecting our generator to grid by
matching with the grid frequency.
a synchroscope is used if our generator speed is less than
grid speed (frequency) the synchroscope rotates counter
clock wise (lag).
if our speed is high the scope needle rotates CW (lead)
if it is equal the needle stops
| Is This Answer Correct ? | 21 Yes | 6 No |
Answer / jock
To ensure the incoming generator takes up load as soon as
the generator circuit breaker is closed.
If synchronism was achieved with the synchroscope
indicating an anti-clockwise rotation the generator would
not take up load and instead would driven by the bus, ie.
reverse powered. If the reverse power is large enough
tripping of the generator is likely to occur.
When manually synchronising a generator to the bus it is
normal to give a quick 'increase' command on the controls
just after the breaker closes to ensure positive power
loading takes place.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / amritpal singh sidhu
I think this is due to the phase sequence, because we use
the sine wave in electrical generation so the sine wave
produced is according to quadrants(In which sine wave is
plotted CLOCKWISE ).
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / vikas wadhwa
In my point of view; in modern turbo-generators there is
already provision of about 5% automatic load command as
soon as gen. breaker is closed thus leaving no chances of
gen. tripping on reverse power. Hence, it will not make any
difference technically whether syncronization is done in
cloclwise or anticloclwise direction.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / anees ur rehman
I hope that answer 2 and 4 are v.good.Normally
synchronisation done at 1/10 frequency of incoming
generator kept higher thans the exisisting source.why.yes
when it is synchronised as generator take load its speed
decreases due to low frequency it will trip so its
frequency is kept 1/10 times more than source
| Is This Answer Correct ? | 5 Yes | 3 No |
Synchronization should be done in CW direction , to avoid reverse power trip , because CW means your alternator speed and voltage is slight greater then grid ,after immediate synchronizing load will delivered to grid , other wise there is change of reverse power trip.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheena mahany
i didnt get anything . be a little bit more clear....
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manav
There are five conditions that must be met before the
synchronization process takes place. The source (generator
or sub-network) must have equal
line voltage, frequency, phase sequence, phase angle, and
waveform to that of the system to which it is being
synchronized.
(source:----wikipedia)
Clockwise mode of operation is a standard.It has been set to
ensure that phase sequence is not reversed while
synchronizing the generators. Otherwise, same thing might
happen as explained in Answer #7.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mukul
synchronisation is done in CW direction coz generator should have voltage slightly more than tha system .. because at tha time of synch system start taking load from generator instantly. to avoid generator speed lower than the rated one this needs to do.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.anandsah
It doesn't matter if you synchronise TG with Grid in cw or anti cw . Just after synchronisation increase the power as soon as possible.
| Is This Answer Correct ? | 0 Yes | 0 No |
What are various power system instabilities and what are their effects on power system operation?
what is the importance of earthing system on the generators big capacity and small?
in single phase converter, the no.of scr's conducting during overlap a)1 b)2 c)3 d)4
how we calculate the dick for a pole?
what is active power and rective power and power factor
What are the major reasons for balancing hydro-thermal mix?
what are the major difference between 3phase 3wire and 3phase 4wire trivector meter?
does not the circulating current in a transformer affect the flux distribution in the transformer core
Whar is the KvA rating of 33Kv substation & actual kv rating of power generaating station.
what will happen power cables laid without gap in underground
why ct mensioned 0.5/5p20 plese any reply to me
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)