Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why synchronization done in clockwise direction?

Answers were Sorted based on User's Feedback



why synchronization done in clockwise direction?..

Answer / shonali

there is no CW and CCW synchronization it depends on the
speed difference

synchronization is connecting our generator to grid by
matching with the grid frequency.
a synchroscope is used if our generator speed is less than
grid speed (frequency) the synchroscope rotates counter
clock wise (lag).
if our speed is high the scope needle rotates CW (lead)
if it is equal the needle stops

Is This Answer Correct ?    21 Yes 6 No

why synchronization done in clockwise direction?..

Answer / jock

To ensure the incoming generator takes up load as soon as
the generator circuit breaker is closed.
If synchronism was achieved with the synchroscope
indicating an anti-clockwise rotation the generator would
not take up load and instead would driven by the bus, ie.
reverse powered. If the reverse power is large enough
tripping of the generator is likely to occur.
When manually synchronising a generator to the bus it is
normal to give a quick 'increase' command on the controls
just after the breaker closes to ensure positive power
loading takes place.

Is This Answer Correct ?    8 Yes 1 No

why synchronization done in clockwise direction?..

Answer / amritpal singh sidhu

I think this is due to the phase sequence, because we use
the sine wave in electrical generation so the sine wave
produced is according to quadrants(In which sine wave is
plotted CLOCKWISE ).

Is This Answer Correct ?    10 Yes 4 No

why synchronization done in clockwise direction?..

Answer / vikas wadhwa

In my point of view; in modern turbo-generators there is
already provision of about 5% automatic load command as
soon as gen. breaker is closed thus leaving no chances of
gen. tripping on reverse power. Hence, it will not make any
difference technically whether syncronization is done in
cloclwise or anticloclwise direction.

Is This Answer Correct ?    4 Yes 1 No

why synchronization done in clockwise direction?..

Answer / anees ur rehman

I hope that answer 2 and 4 are v.good.Normally
synchronisation done at 1/10 frequency of incoming
generator kept higher thans the exisisting source.why.yes
when it is synchronised as generator take load its speed
decreases due to low frequency it will trip so its
frequency is kept 1/10 times more than source

Is This Answer Correct ?    5 Yes 3 No

why synchronization done in clockwise direction?..

Answer / rajas

Synchronization should be done in CW direction , to avoid reverse power trip , because CW means your alternator speed and voltage is slight greater then grid ,after immediate synchronizing load will delivered to grid , other wise there is change of reverse power trip.

Is This Answer Correct ?    2 Yes 0 No

why synchronization done in clockwise direction?..

Answer / sheena mahany

i didnt get anything . be a little bit more clear....

Is This Answer Correct ?    1 Yes 1 No

why synchronization done in clockwise direction?..

Answer / manav

There are five conditions that must be met before the
synchronization process takes place. The source (generator
or sub-network) must have equal
line voltage, frequency, phase sequence, phase angle, and
waveform to that of the system to which it is being
synchronized.
(source:----wikipedia)

Clockwise mode of operation is a standard.It has been set to
ensure that phase sequence is not reversed while
synchronizing the generators. Otherwise, same thing might
happen as explained in Answer #7.

Is This Answer Correct ?    1 Yes 1 No

why synchronization done in clockwise direction?..

Answer / mukul

synchronisation is done in CW direction coz generator should have voltage slightly more than tha system .. because at tha time of synch system start taking load from generator instantly. to avoid generator speed lower than the rated one this needs to do.

Is This Answer Correct ?    0 Yes 0 No

why synchronization done in clockwise direction?..

Answer / p.anandsah

It doesn't matter if you synchronise TG with Grid in cw or anti cw . Just after synchronisation increase the power as soon as possible.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

why need of ac exietation in alternater.

2 Answers  


An input device is interfaced with Intel 8085A microprocessor as memory mapped I/O.The address of the device is 2500H.In order to input data from the device to accumulator,the sequence of instruction will be

1 Answers   GATE,


FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER DIFFERENTIAL PROTECTION DOES NOT OPERATE???

10 Answers  


what are factors to be consider in electrical installation like load factor,diversity factor .....

0 Answers  


How is operate breaker failure scheme in substation

0 Answers  


Size of the power cable like 1.5,2.5,4 sq.mm which area calculated from whick area or how specified the size?

1 Answers   MRF,


Why we should use delta connection in primary and star connection in an distribution transformer, which converts 400v a.c. voltage to 33kv.

15 Answers   ABC, Kirloskar, Sify,


What is the basic difference between directional and non directional over current protection?

1 Answers  


In induction machine when the load increase the current will increase .why? what is the relation ship between the sleep and current drown by stater?

1 Answers  


why transformer do not rotate?

3 Answers  


What is meant by harmonic distortion?

0 Answers  


7. A resistance of 30 ohm is connected across 240v supply. If a resistance R ohm is connected in parallel with 30ohm resistor across the same supply, the current drawn becomes triple of original one The unknown resistor R is

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)