why synchronization done in clockwise direction?
Answers were Sorted based on User's Feedback
Guys , i think , it basically depends upon the incoming
source. When u r synchronising grid with a running
generator, u need to synchronise in anti clockwise
direction, Grid being a bigger source shall supply power to
small source initially. If u r synchronising generator with
a already runing system, it shall be done in clockwise
direction as clockwise direction shows higher speed of
incoming generator, which in turn shows the load taking
capability of the incoming source.
Is This Answer Correct ? | 5 Yes | 6 No |
Answer / gunasekaran
IF WE do ccw direction it is reverse power condition so
revese power relay is operate and getting trip
Is This Answer Correct ? | 3 Yes | 4 No |
A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram
I need a 33/690V Dry type transformer.How to select IP class for this transformer.This will be an outdoor transformer located in a highly polluted environment.
What is the distance between each insulator in 33kv transformer and how can it calculate
What is an ideal transformer?
i want to make an elec generater with only 12v car battery car alternater and 12 volt motor ..... will the battery charge and give power at same time with out over charging the battery?
current transformer balance the power level on both sides. e.g in case of step up, at secondary side voltage rise but current decrease and vice versa in case of step down transformer. but how this power level remains same in case of current transformer and voltage transformer
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
why so voltage is same in parallel circuits and current is same in series ckt?
sir can you operated Transformer on frequency from that for which is design?
Why are tertiary windings used in transformers?
Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?
How to select a D.G set for calculated load of 110kW..?