Can we use 1.1x 2 split air-conditioning at a same time in 2kw power loadar
Answer / b.janardhana rao
1.1 tr air conditioner 2 no.s are not used at the same time on 2 Kilo watts load. because compressor will start initially it will take High amps. so we can use alternatively.
| Is This Answer Correct ? | 2 Yes | 1 No |
can we light the mercury vapour (tube light)with out a 1).starter and 2).choke in our homes if yes explain how?
what is the difference between on line UPS & INVERTOR
i want to trigger ATS (Mains +Generator )from external system could any body help me in this regard ?? is it posible if yes please tell me how?
If the circuit breaker will not close or it will trip, what will you do?
we want to feed 3 phase supply to 70 ton AC load.what will be the size of (3 phase)cable require.
What is neutral and how to produced
with 3 phase board on a 63 amp rcd is it ok to have 6 electrical showers 2 on each phase and what problems could happen
what is relation between torque and speed / rpm?
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
CAN WE CALCULATE THE NEGATIVE SEQUENCE AND ZERO SEQUENCE REACTANCE OF A GENERATOR USING ONLY ITS RATED VOLTAGE, KW, PF AND SYNCHRONOUS REACTANCE??? IF YES, THEN HOW??
It is advisable 2 use auto-transformer if transformation ratio is-a)110KV/11KV,b)230kv/110kv,c)110kv/66kv,d) 400kv/230kv
which type of breaker sould be used for different level of voltage ? (i.e at 11 Kv, 33 Kv, 66 Kv....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)