Answer / gomathi sankar
Calibration of instruments is nothing but comparing the
actual value of the instrument which u use with the
standard value of that instrument model.
| Is This Answer Correct ? | 29 Yes | 2 No |
Answer / raffi
Calibration procedure:
calibration equipment: calibrator with handpump
For ex: Range of Transmitter is 0-100psi
Step1: connect the calibrator to the transmitter
Step2: connect the multimeter in series with transmitter to
verify the transmitter o/p in mA
step2: Apply the pressure to the transmitter by hand pump
in calibrator
Step3: compare whether both calibrator and the transmitter
showing the same value.if you applied 50 psi throuhg the
calibrator then the transmitter should have to show the
same value.If you find any error.Do the zero/span
Adjustment.by adjusting the zero/span screw
increasing/decreasing
step4: compare the transmitter and calibrator as per follows
calibrator Transmitter Transmitter o/p
in psi in psi in mA
0 0 4
25 25 8
50 50 12
75 75 16
100 100 20
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / vasu
Calibration of instruments is nothing but comparing the
actual value of the instrument which u use with the
standard value of that instrument model......
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / bill
If an instrument operates throughout it's full range
with linearity and porportionality when compared to
an NIST Standard, it is considered in calibration
( National Institute of Standards and Technology )
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / joseph
cALIBRATION IS NOTHING BUT THE COMPARISON BETWEEN THE
STANDERED VALUE AND THE MEASURED VALUE.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / sakthisithardhan
Calibration is the process of to set an instrument to show
the reading in between allowable scale....
example 0-10V meter
if ponter shows <0 means v've to calibrate it to show exact
0.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / rajiv mehta
To check whether the instrument in use is with in the
standard parameters
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / narenkumar1985
calibration equipment: calibrator with hand-pump
1: connect the calibrator to the transmitter
2: connect the multimeter in series with transmitter to
verify the transmitter o/p in mA
3: Apply the pressure to the transmitter by hand pump
in calibrator
4: compare whether both calibrator and the transmitter
showing the same value.if you applied X psi through the
calibrator then the transmitter should have to show the
same value.If you find any error.Do the zero/span
Adjustment.by adjusting the zero/span screw
increasing/decreasing
5: compare the transmitter and calibrator as per follows
with a desired range of an instrument with o/p 4-20mA
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vivek saini
CALIBRATION of INSTRUMENT IS A TESTING OF ACTUAL VALUE ie:- value which is calculated WITH THE NATIONAL INSTITUTE OF STANDARDS AND TECHNOLOGY (NSIT) VALUE GENERALLY DONE FOR CHECHING THE ACCURACY OF INSTRUMENT.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rafiq
calibration is nothing but the "testing" . it compares the
actual value to real value and realise that value takes the
decisions
| Is This Answer Correct ? | 2 Yes | 3 No |
what is thermocouple output
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
Hi buddies! i am facing a problem and if someone could help me it will be an immense pleasure to me. we have compect logix PLC 1769 2L AO module to Heat @ 52 to 56 Deg C .So if anyone can do please help me out with this problem.I'll be highly grateful.
what is the function of 3 way manifold valve in a closed loop system?
what is the PC interface and software for connection to ABB logic module “ LM011-CE18RAC “ ( for Programming ) ??
What is difference between magnetic flow transmitter & Electromagnetic flow transmitter?
yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculation result is bad) in manual they mentioned reasion That the output goes to the value set by hardware failure mode jumper. How can solve this problem ? anybody can say solution
who to convert dc to ac
TEMPERATURE VARIATION FOR FREQUENTLY.
Control valve Flow characteristic. How the equal percentege curve form?
What are advantages and disadvantage of the ac supply load cell?
IS THEIR ANY AGEING EFFECT ON FLOW NOZZLE, ORIFICE, MANIFOLD, OR TRANSMITTER ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)