yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculation result is bad) in manual they mentioned reasion That the output goes to the value set by hardware failure mode jumper. How can solve this problem ? anybody can say solution
Answer / carl_ellis
In the manual (from which you cited) the user action for
error 15 is 'contact service personnel'.
You can try that, but I suspect that it means, for all
practical purposes, replace the transmitter. I don't know
if Yoko offers a spare 'puck' that can be replaced in order
to salvage the housing and display, or not. You'll have
to ask.
You might try cycling power to it to see if an electrical
spike on the loop wiring adversely affected the processor,
and cycling the power might re-initialize it, but the
likelihood of success is very small.
When a transmitter goes to fail-safe mode, it's usually the
last act of the last performance, the actors are clasping
hands, and taking a final bow before the show closes.
tell 'em Carl sent you
Is This Answer Correct ? | 3 Yes | 0 No |
We are used CENTUM CS3000 of YOKOGAWA. please tell me how to simulate wihtout FCS and vnet.
What is seeback effect?
Which type of pressure can be measured by these elements?
Why Flow measure in Square-root?
wt is cold junction compensation
I am pujita completed Electronics and Instrumentation Engineering.As a fresher i am going to attend the interviews.Could anybody guide the topics/questions covered mostly in interviews.
What is purpose of shield wire?
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?
loop chech tools list
Reasons for using seal pots:
During the design and engineering of a process plant, a good designer should plan for ____________, ___________ and ____________ aspects of the plant
Can a pneumatic control valve work without positioner?