Why a starter is used for a motor?
Answers were Sorted based on User's Feedback
Answer / priya
starter is mainly used to limit the starting current ,which
is very much greater i.e 4 to 5 times at the time of
starting.we have to limit this.otherwise it may damage the
other equipments also.for that we are using starter ..
it limits the current by adding resistance in the circuit.
various types of starters available.
2 point,3 point,4 point types are widely used.....
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / v.selvakumar
if u r using stat delta in induction motor it will reduce
stating current .57(aprrox),in the case of d.c motor
application it limit statrting current according to emf
equation E=v-iara
ia=v-E/ra
where ra aramature is very less.normally in the order of
ohms.at starting E is zero.so ia=v/ra so current will be
high.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / anuj kumar
During Starting Motors take a very high current i.e.-5 to 7
times of its normal rating which can cause damage the
machine due to excessive also cause a sharp voltage dip
which is unacceptable for other equipment connected to same
line.
To prevent from this high starting starters are used
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / divya
dc motors r self started motors.but as d initial resistance
is small ..by ohms law v sa dat current inc.so inord 2
reduce d inflow of current n 2 run the motor in safe zone v
vl use this starter.
v can c it in 3-pt.starter,4-pt starter.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / michael angelo borjal
The starter motor converts electrical energy to mechanical energy and is mounted on the cylinder block in a position to engage a ring gear on the engine flywheel.
| Is This Answer Correct ? | 0 Yes | 0 No |
starter are use to reduce the high starting current and provide protection against under voltage & overload condition
in dc motor 3-pt & 4-pt starter are use. the resestance are ude to limit high starting current & nvc are use to other protection.
in ac motor dol ,star-delta,& autotransformer are use.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / boopathi
Starter are basically used to reduce the starting current.
I = ( V - Eb ) / R.
Where I is the field winding current,
V the voltage and Eb - Back up emf and R the winding resistance.
During starting Eb = 0, and R - a very small resistance.
so, as the high current passes through the winding, there is
chance for winding to burn out. When the motor attains the
normal speed it generate the back up emf, enough to reduce
the winding current.
To avoid this we need to reduce the voltage(V) or increase
the winding resistance. Since the reduction of supply
voltage is difficult to attain, a starter is used, which
will push high resistance during starting and gradually
reduces and fully removed from the circuit when the motor
attains the full speed.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / selva ganesh
IF YOU GIVE SUDDENLY MAXIMUM (FULL) CURRENT APPLIED ON
MOTOR MEANS THE MOTOR COIL SYSTEM WAS TOTALLY DAMAGED.SO
WILL USE THE STARTOR MEANS TO GIVE THE CURRENT IS
UNIFORMELY (CURRECTLY).
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jodha
ac motor thr rotor current dirctly proportional to slip
at the moment of starting the rotor is standstill, it means
the slip has the it is maximum value so therotor current
also maximum so,it cause rotor is burned. to avoid it we
must provide the stater.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the definition of Nominal current or voltage
What do you mean by pull of electromagnet?
Though transformer consist winding which usually cause reactive power change in both generator and motor but it wont affect reactive power passing through transformer why?
what is the difference between 11kv and 13.8 kv? why we can't used one of these 2 sources?
what is the difference b/w bus reactor and line reactor?
which is more danjerous high voltage or high current
what is dc transformer? how it work?
what is the relation between reactive power and power factor for the what is the limit of reactive power and power factor
What is the advisble power factor to be maintained in grid connecting power generation plnats without any effecting the generator.
3 pahase 750kva Running 2 DG sets in 35 mints.525ampers. and 616 kw how much fuel consumption in Generator.what is the formula.
1 Answers Delite Systems Engineering,
how to calculate AH of a battery?
1 Kva = How many KW
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)