Answer / anu
all are telling its 0.9 to 1 but nobody is not telling how
ur maintain that? what are the technics using for that?
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ronald
power factor regulation is done by connecting the Capacitor
bank- Dry type (Auto- by fixed steps or by manual
regulator) to the main Distribution board MDB.(remember the
baiscs and how cos phi is calculation is made)
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mphiremath
always pf should maintaine 0.90 to 0.96. It avoids the more
energy consumption.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / thowsif_emerson_csm team
The Power Factor Should be above 0.9 as per BESCOM
Starndard.
If the PF is bellow 0.9 then in Karanataka thier will some
amount of Penalty i.e P.F Penalty,they will add up this
amount in the monthly Electriccity Bill issued KPTCL.
So to avoid this we sholud maintain the PF Above 0.9 Lag....
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sarang hivarkar
P.F can be maintained by using HHF Harmonic Hybrid Filter (HHF) panel and APFC panel.p.f should be 0.9 to 1 required in Industry.we are used HHF panel to reduce Harmonic distortion current Harmonic in the plant and maintained the P.F.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ravi.hs
for any industry you have keep maintaining the pf @ 0.95
that is the std .
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / rajkumar n
power factor is the ratio of true power/apperent power*cos
fay is called power factor.. loads are three types
1.Resistive Load
2.Inductive Load
3.Capacitive Load
Inthis load Resistive load is Unity Powerfactor
Inductive load is Lagging powerfactor
Capacitive Load is Leading Powerfactor
PowerfactorImprovement:
1.Static Capacitor
2.Synchronous condensor
3.Phase Advansor
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shasheen
In our orgn we are maintaining 0.98 by APFC at L.T side
and H.T Capacitors parallel to motors and H.T bus
capacitors. If our power factor is less than 0.95 in A.P
State elect board will impose fine Our running load is
35 MVA OF Cement Plant
| Is This Answer Correct ? | 1 Yes | 0 No |
What is cable size of motor if starting current is 15.6 Amperes??
why there using acb enclosure in big buildings
Which is the oldest hydropower plant in india?
How to select a cable size according to load
What is pi controller?
what are earthing material
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
Explain mechanical rotational system?
Define settling time.
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
why the frequency and voltage in india is 230v and 50HZ. when compared to USA say 110v and 60 HZ.
what is the capacitance of a single conductor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)