What is the power factor you maintain at ur organization?
Answers were Sorted based on User's Feedback
Answer / r.prabhu
powerfactor is a cosine angle between voltage and current.
In industries powerfactor maintained is most important one.
loads are three types 1.Resistive Load
2.Inductive Load
3.Capacitive Load
Inthis load Resistive load is Unity Powerfactor
Inductive load is Lagging powerfactor
Capacitive Load is Leading Powerfactor
PowerfactorImprovement:
1.Static Capacitor
2.Synchronous condensor
3.Phase Advansor
| Is This Answer Correct ? | 137 Yes | 17 No |
Answer / ravi
power factor is the ratio of real power to apparent power
generally p.f must be 0.95
| Is This Answer Correct ? | 88 Yes | 9 No |
Answer / rk
we are maintaing the power factor between 0.95 to 0.98.
the most economical power factor is 0.96.
if your pf is below 0.9, electrical board authorities will
impose a penalty.
| Is This Answer Correct ? | 84 Yes | 10 No |
Answer / h.s. raveesh
Maintaining Unity powerfactor is impossible in industries
or in other places. but research is going on for sucessful
use of unity powerfactor
| Is This Answer Correct ? | 29 Yes | 6 No |
Answer / selvan
Power factor is ratio of real power to apparant power.In
industries maitain the powerfactor is important one.But not
maintain the powerfactor in unity, Loads varied form time
to time.In industries induction motors and tubelights
mostly used. This are inductive loads,this loads create
lagging powerfactor.So to improve the powerfactor by using
static capacitors,syncronous condensor and phase advanser.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / christopher
power factor should be 0.90 to 0.99,should not be more than
1 (unity power factor)
| Is This Answer Correct ? | 14 Yes | 7 No |
Answer / vinothbabu.k
THE BETTER POWER FACTOR MAINTAINED IS 0.95 TO 0.85,IF BELOW
0.85 THE ELEC BOARD WILL PUT PENALTY,IF WE MAINTAINED ABOVE
0.95 THE BOARD WILL GIVE U THE INSENTIVE FOR THAT.
| Is This Answer Correct ? | 13 Yes | 6 No |
In our generating power station we get electric shock in the battery bank, what will be the reason?
What's the difference between non break power supply and non break non short break power supply
how to select cable size for three phase?
WHY WE ARE DOING THE EARTHING IN A SYSTEM. SOME PEOPLE ARE TELLING FOR PROTECTION. WHAT PROTECTION GIVE ME THE CORRECT ANSWER.
A.V.R maintains the voltage of a generator when it is in island mode but when the generator is synchronised with grid it maintenance the P.F,how it happens please any body explain it in detail.
what is lowest system voltage?
what is the safe meggar values for motor, transformer HT, LT and Cables? IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace. why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
what is the maximum load sutiable from earth to phase and what is the max voltage earth to phase suitable
Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.
what is the problem when i want to close a circuit breaker by local position it closes well.but when i close it in remote position it trips
what is the lightning arrester rating for 3.3kv system voltage
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)