What is the power factor you maintain at ur organization?
Answers were Sorted based on User's Feedback
Answer / shiva
power factor is cosine angle of voltage & current in vector diagram,& is ratio of real power to apparent power.. we maintain in our organisation as installation of capacitor bank. its valve in between 0.95 to .99. but valve of p.f. below the 0.9 & above 1.0 organisation get penalty charges as per Msedcl act.. maintaining p.f. means keeping resistance of circuit unity.or balance the resistance of inductive load to resistative load in circuit by capacitance load.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / n nagaraju
0.8 TO 0.95
power factor is the ratio of real power to apparent power
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / nithyanandam
Power factor in most industries are 0.93 to 0.99.....
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anil
for ideal power system, power factor is unity(1),
but practcally it is very difficult to archive. but this
value is effected by reactive load.
Power is generated at power factor of .8 to .85 .
so we can maintain the power factor at .8 to .85
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagaraju.n
hi
(0.8 to 0.9)in average of three types of lode
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / selvan
we are maintaining the PF in factory at unity without the
help of APFC unit.we miantain the PF below 0.95 lag for
avoid EB penalty.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shiraz khan
yes, it is true that we can't maintain the power factor
nearer to 1, but in CAPACITIVE or in the case of RESISTIVE
load it is possible that we can maintain the power factor
from 0.9 to 0.96. And normally in our homes we can easily
maintain the power factor, because we didn't normally uses
the 3 phase inductive motors, or any othe heavy inductive
load like as in factories.
| Is This Answer Correct ? | 0 Yes | 0 No |
In cement industry maintain pf near by unity if power taken from SEB by using APFC for LT load and bus capacitor for HV system. Monthly average pf is .991 to .995.SEB generally offer insetive of 1% above .97 pf in some state.
But if CPP is there maintaining .95 to .98.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is meaning of bus riser
why restricted earth fault protection can not operate for phase faults??as there will be a current in secondary of ct,when a phase fault occurs!
what is a starter ??
one kva is equal to how much amps?
What is GIS (Gas Insulated Switchgear)
Define availability (operational)?
what is POTT and PUTT explain?
what is meant by impedance & transient protection?
This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.
What type of pipe material G.I or M.S is used for sprinkler system?
what is reverse power relay brief explanation and in b/w where it is connected
what is the effect of constant power factor to the voltage regulation
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)