What happen when the AVR of the generator fails? Will it cause
power instability and total failure of the alternator?
Answers were Sorted based on User's Feedback
Answer / sundar m
AVR is the Automatic Voltage Regulator which is used to keep
the alternator terminal voltage to be constant whenever
voltage drop occurs....by varying the excitation and the
power supplied to the alternator with turbine...If AVR fails
then the voltage level of the alternator fails to be
constant.so the machine will comes out of synchronism.....
Some protection systems are there...to trip the machine when
the AVR fails so dont think like intelligents....
Is This Answer Correct ? | 34 Yes | 2 No |
Answer / jagan
When AVR fails a protection called Field Failure protection will come into picture and trip the generator.
When AVR trips the machine draws reactive power from grid n continue to run as Induction Generator but above synchronous speed which might damage the turbine.
It has 2 time delays
If Failure of field is associated with under voltage which might happen due to severe fault near the generator and AVR might trip not able to maintain the voltage, the generator is tripped instantaneously.
If the AVR fails and there is no U/V, a delay of 1-2 sec is incorporated hoping the AVR might restore.
PROTECTION ENGINEER 11 YEARS EXP
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rakesh.a.d
When AVR fails,the excitation to the generator fails and the alternator acts as an induction generator taking reactive power from the grid
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheikh
AVR is Automatic voltage regulator. AVR is a vital part of Alternator if Avr has become failed than alternator should gone at shutdown on undervoltage or No volltage safety. its make clear that whenever your enginator reduce the Rpm by any other fault than alternator also going on undervoltage safety that time AVR cannot balanced the determined voltage or Set point voltage.
Is This Answer Correct ? | 5 Yes | 4 No |
Generally if there is failure of AVR , excitation will switch over manual mode .
Is This Answer Correct ? | 1 Yes | 0 No |
Further ,the ' loss of excitation relay ' should act to trip . If it does not and the prime mover is still working , then the gen will run as induction generator . It may disturb stability as the pf is very low .
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaizad
Generally big power plants have a feature by which the manual rehostate follow AVE. So when Ave trips there is no sudden variations in power and by manual actions can be taken to avoid generator transformer overfluxing by keeping V/for ratio constant
Is This Answer Correct ? | 0 Yes | 3 No |
How do you consider that you can improve and what assistance do you need to achieve this
dear sir i have completed one year post diploma certificate in thermal power engineering from national power training institute durgapur ...plz suggest me for power sector job
What is reheated protection
What are the special criteria under which FD fans are switched off during MFT.
In one plant id fan and fd fan are used for boiler. boiler is used to heat water after some days they install one tank to heat water by hot flue gases coming out from boiler and then hot flue gases are used to heat the air coming from fd fan before leaving out from chimney . but hot flue gases are not coming out from id fan what might be the reason?
What should be the neutral and body grounding sysytem for grid (132 KV) parallel generators (440 volts)?
Why superheated are started before I'd and rd fan?
What happen when the AVR of the generator fails? Will it cause power instability and total failure of the alternator?
How to calculate power press toneage
what are the steps of syncronizing the generator with an infinite grid?
what is natural frequency of turbine shaft .
Difference between directional earth fault and non-directional earth fault