Answer / sundar m
AVR is the Automatic Voltage Regulator which is used to keep
the alternator terminal voltage to be constant whenever
voltage drop occurs....by varying the excitation and the
power supplied to the alternator with turbine...If AVR fails
then the voltage level of the alternator fails to be
constant.so the machine will comes out of synchronism.....
Some protection systems are there...to trip the machine when
the AVR fails so dont think like intelligents....
| Is This Answer Correct ? | 34 Yes | 2 No |
Answer / jagan
When AVR fails a protection called Field Failure protection will come into picture and trip the generator.
When AVR trips the machine draws reactive power from grid n continue to run as Induction Generator but above synchronous speed which might damage the turbine.
It has 2 time delays
If Failure of field is associated with under voltage which might happen due to severe fault near the generator and AVR might trip not able to maintain the voltage, the generator is tripped instantaneously.
If the AVR fails and there is no U/V, a delay of 1-2 sec is incorporated hoping the AVR might restore.
PROTECTION ENGINEER 11 YEARS EXP
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rakesh.a.d
When AVR fails,the excitation to the generator fails and the alternator acts as an induction generator taking reactive power from the grid
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheikh
AVR is Automatic voltage regulator. AVR is a vital part of Alternator if Avr has become failed than alternator should gone at shutdown on undervoltage or No volltage safety. its make clear that whenever your enginator reduce the Rpm by any other fault than alternator also going on undervoltage safety that time AVR cannot balanced the determined voltage or Set point voltage.
| Is This Answer Correct ? | 5 Yes | 4 No |
Generally if there is failure of AVR , excitation will switch over manual mode .
| Is This Answer Correct ? | 1 Yes | 0 No |
Further ,the ' loss of excitation relay ' should act to trip . If it does not and the prime mover is still working , then the gen will run as induction generator . It may disturb stability as the pf is very low .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaizad
Generally big power plants have a feature by which the manual rehostate follow AVE. So when Ave trips there is no sudden variations in power and by manual actions can be taken to avoid generator transformer overfluxing by keeping V/for ratio constant
| Is This Answer Correct ? | 0 Yes | 3 No |
why the Steam Turbine(20MW)center line and gear box center line not in same elevation during coupling alignment ?
3 Answers Greenesol Power Systems,
Difference between islanding and house load operation.
What is reheater protection based on what mft will be act on RH protection
what is under voltage protection 27
what are the major duties of a instrumentation engineer in a power plant.?
which safety valve will open first if steam is not been supplied to turbine.
what is restricted earth fault explain in details
why drum level falls when one of the running coal elevations tripped?
What are the motors used in a thermal power plant? (With type and ht/lt) What voltage levels are used in a thermal power plant?
what is absolute separator, how it works, what are the types in it
I want to build 100 megawatt hydel dam. What does mean, 100 MW per hour? then how many electric bulb of 100 Watts the dam would lit?
Why high pressure turbines are single flow
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)