How can you calculate in detail the VA burden of current
transformer used for Restricted earth fault protection?
Please understand that the CT required here is Class PX or
X. Also please show the calculations for knee point vtg,
stabilizing resistor, magnetising current.
Answers were Sorted based on User's Feedback
Knee Point voltage is nothing but a point at which the CT
saturates. Thats why its always better to design the CTs
which can operate without saturation even at a voltage
appears in the CT during fault condition. Pls find below
the following formula for calculating the Knee point
voltage.
Vk=2If(Rct+2Rl).
where, If is the current refected to the CT secondary
during fault condition,
Rct is the resistance of the CT which can be adopted by
means of a thumb rule considering the CT ratio,
Rl is the lead resistance i.e. sum of the resistance of the
wire connected between the relay & CT and Impedance offered
by the internal circuitary of the relay
For PS class CT's designed considering the above,burden is
not applicable.
| Is This Answer Correct ? | 7 Yes | 0 No |
Restricted earth fault protection is a differential scheme,
with CTs on the transformer neutral and phase leads. The
phase CTs are connected together in parallel & then
paralleled with the neutral CT. The resticted earth fault
(REF) relay is connected across the paralled CT circuits.
The relay is either a voltage operated device (eg Alstom
MFAC14)or a current relay with an external setting resistor
(eg Alstom MCAG14). In either case, the scheme is set at a
voltage based on the maximum voltage that is developed at
the relay for an external fault. A practical setting is
50% of the CT knee point voltage, if full info is not
available.
| Is This Answer Correct ? | 3 Yes | 3 No |
For PX class CTs , the burden is not normally mentioned .
There the CT is defiened based on the CT kneepoint
voltage , magnetising current etc . The burden is mentioned
in class P CTs
In PX class CTs the kneepoint voltage is normally based on
the max fault current and a diamensioning factor based on
system X/R ratio
| Is This Answer Correct ? | 3 Yes | 3 No |
capacitor is load free component but why ampare meter shows current when capacitor bank breaker close?
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
how the ac voltage are selected like 220v,415v,750v,1000v& 1.KV,6.6KV,11KV,33KV,66KV,132KV,220KV & why these are selected like these orders
difine electrical ballast in HPSVL
Why we need to carry out knee point voltage test of current transformer ?
How we Use DC Power in Transformers? is it possible ?
Why OLTC(On Load Tap Changing)transformer is not recomended for improving voltage instability?
What is the PI test stand for transformer and what is the producer to do this test?
Why neutral grounding Transformer provided for generator?
Explain the experiment on ward leonard method of speed control of a dc shunt motor.
What will happen if an AC induction motor is applied with DC voltage?????????Kindly give all the posssible answers...
what is derating?, why it is neccesary, it is same for all means for drives, motors,and cables.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)