Answer / william lobo

Knee Point voltage is nothing but a point at which the CT
saturates. Thats why its always better to design the CTs
which can operate without saturation even at a voltage
appears in the CT during fault condition. Pls find below
the following formula for calculating the Knee point
voltage.

Vk=2If(Rct+2Rl).

where, If is the current refected to the CT secondary
during fault condition,

Rct is the resistance of the CT which can be adopted by
means of a thumb rule considering the CT ratio,

Rl is the lead resistance i.e. sum of the resistance of the
wire connected between the relay & CT and Impedance offered
by the internal circuitary of the relay

For PS class CT's designed considering the above,burden is
not applicable.

Is This Answer Correct ?    7 Yes 0 No

How can you calculate in detail the VA burden of current transformer used for Restricted earth fau..

Answer / williamlobo

Restricted earth fault protection is a differential scheme,
with CTs on the transformer neutral and phase leads. The
phase CTs are connected together in parallel & then
paralleled with the neutral CT. The resticted earth fault
(REF) relay is connected across the paralled CT circuits.

The relay is either a voltage operated device (eg Alstom
MFAC14)or a current relay with an external setting resistor
(eg Alstom MCAG14). In either case, the scheme is set at a
voltage based on the maximum voltage that is developed at
the relay for an external fault. A practical setting is
50% of the CT knee point voltage, if full info is not
available.

Is This Answer Correct ?    3 Yes 3 No

How can you calculate in detail the VA burden of current transformer used for Restricted earth fau..

Answer / william lobo

For PX class CTs , the burden is not normally mentioned .
There the CT is defiened based on the CT kneepoint
voltage , magnetising current etc . The burden is mentioned
in class P CTs

In PX class CTs the kneepoint voltage is normally based on
the max fault current and a diamensioning factor based on
system X/R ratio

Is This Answer Correct ?    3 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

1 tr is equal to how many Kw .is there any specific formula for this to get the result .

13 Answers   Cipla, LG, NSN,


List the materials required for Pipe Earthing.

2 Answers  


why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.

7 Answers  


What is the reason of using bus-bars on the secondary on the LT transformers?

2 Answers  


cost of operation of which plant is least?

6 Answers  






sir pls tell me . our ct specifications are 120/5 ,2 core , 0.2 and 5p10 class , 30va and 30va buden. insted of 30 va i want use 15 va. can i use?

0 Answers  


When we need start the motor by method of star delta which size (KW or HP)motor should must be operate in Star Delta Method,

3 Answers  


Motor and transformer working with same principle so why motor rotates while transformer not?

7 Answers  


1ampear me kitna watts hota hai aur elcb ka pura naam kya hai

18 Answers   Al Khayyat, Alpha G, BEC, Bhel, CGS, Electrical, Fiem, Firmenich, HLG Habtoor Leighton Group, Jash, Kandia, Maruti Suzuki, Minda, NTPC, ONEIC, Pace Process Controls, SMTC, SR, Sunrise Electrical, Sushil Enterprises, Suzlon, Voltage,


Two CTs 1600/1 and 35/1 are in series. while checking the ratio test of a CT(1600/1),same 1600A will also pass through the CT having ratio 35/1. Will it be harmfull to the ct(35/1),if yes , what will happen.CT secondary is shorted

3 Answers  


UPS battery Back time = no.of Batteries * Ah of the Battery / output KVA * 130 ? what is the 130 means ? can any one help? because all are using this formula how its came 130?

2 Answers  


What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)