I have 800 Amps MG Fix type breaker It is in on line & it
has been given only UV (under voltage)coil connection for
tripping purpose.now it is not working properly means its
getting tripp so how can i replace it or how can i rectify
the problem without destrubing my load??????????
Answers were Sorted based on User's Feedback
Answer / sandeep khaire
Short the UV relay contacts used in wiring. Then replace
the UV relay & its contacts.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / karthik
Check with the wiring diagram of the panel and connect the
two wires going to the relay trip coil to a constant
supply.then remove the relay.
Is This Answer Correct ? | 0 Yes | 0 No |