How can you calculate in detail the VA burden of current
transformer used for Restricted earth fault protection?
Please understand that the CT required here is Class PX or
X. Also please show the calculations for knee point vtg,
stabilizing resistor, magnetising current.
Answer Posted / williamlobo
Restricted earth fault protection is a differential scheme,
with CTs on the transformer neutral and phase leads. The
phase CTs are connected together in parallel & then
paralleled with the neutral CT. The resticted earth fault
(REF) relay is connected across the paralled CT circuits.
The relay is either a voltage operated device (eg Alstom
MFAC14)or a current relay with an external setting resistor
(eg Alstom MCAG14). In either case, the scheme is set at a
voltage based on the maximum voltage that is developed at
the relay for an external fault. A practical setting is
50% of the CT knee point voltage, if full info is not
available.
| Is This Answer Correct ? | 3 Yes | 3 No |
Post New Answer View All Answers
What is the implications when 600 hp motor is started when the unit is running with Transformer of capacity 1500 KVA and DG set of 1000kva
Define corner frequency?
ELECTRICAL ENGINEER TEST IN FEWA ANY ONE HAVE KNOWLEDGE ABOUT THIS?????????
What is the difference between security constraint unit commitment and security constraint optimal power flow?
explain the functions of main isolation switches
with out colour codeing on conductor how can be find what is r,what is b,what is y phases.....
What is grid collapse? what is the reason for it?
What is the ideal position cooling fan inside the dc motor?
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
What is vaccum currcuit breaker.define with cause and where be use it device?
When a single pase capacitor run motor- run on 230vac and Case(1)run with 8 Mfd 250 vac.capacitor , Case( 2) run with 8 Mfd 400vac capacitor. What is difference between both case regarding power ,efficiency etc?
difference between servo motor and synchronous motor
How to Calculate the Fault Level of Electrical Installation
1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?
where can i get vijaya electricals limited in hyderabad interview auestions can u give me the website address plz