how will i find Transformer rating if supply voltage is
11k.v and how will i find incomer if transformer rating is
12MVA
Answers were Sorted based on User's Feedback
Answer / subhash sapkal
12MVA Tranformer connect in 11KV linne . 1>primery side
curret is =< 1090A
2> same trasformer in 33KV primery current is =< 363A
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / koraim
you have to know two parameter out of these (Power ,
voltage & Current) as a basic then you can get whatever u
want.
if the transformer is 12 MVA and 11 kV and assuming that it
is 3 phase, then the current is 630
| Is This Answer Correct ? | 2 Yes | 0 No |
How we calculate airgap between phases & terminal box of the transformer? any formulae.
what type of transformer used in soft ware parks its distribution or power transformer. like 1800 kva
cause of failure of transformer bushes
Three phase alternators are connected in star connection why?
How dc generators direction can be reversed ??
2 Answers GPSC Gujarat Public Service Commission,
why effective resistance should be more than static resistance in transmission line?
what happens if generator is running leading power facotor?
ROC converges if pole and zero lies inside a) origin b) z=1 c) pole d) zero ? Explanation please? if ROC does not converges then?
how dc generator produce voltage initially?
How to calculate ant test the burden of Current transformer
What is stacking factor? What is its approximate value?
What is disc insulator and it's application..?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)