Knee Point voltage is nothing but a point at which the CT
saturates. Thats why its always better to design the CTs
which can operate without saturation even at a voltage
appears in the CT during fault condition. Pls find below
the following formula for calculating the Knee point
voltage.
Vk=2If(Rct+2Rl).
where, If is the current refected to the CT secondary
during fault condition,
Rct is the resistance of the CT which can be adopted by
means of a thumb rule considering the CT ratio,
Rl is the lead resistance i.e. sum of the resistance of the
wire connected between the relay & CT and Impedance offered
by the internal circuitary of the relay
For PS class CT's designed considering the above,burden is
not applicable.
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
direction of tarbine& genrator
How is efficiency of DG set calculated? At many places I found the efficiency to be mentioned in percentage. But at some other places I found kWH/ litres. I want to know how dimensionless percentage value is arrived at?
what is the difference between earthing and unearth
hi frnds what is meant by harmonics & what is meant by third hormonics,where its will occur ?thank u
What is stepper motor?
Both generator parallel condition shared load equally but one genrator taking ampere more than the other what are all the causes to make like this
What is pi controller?
what is stper motor
what is the use of commutator in dc motor if we supply ac ? commutator is used to convert ac to dc.and it is used to arrange the flux in unidirectional in case of dc supply. if we give ac as supply to dc motor what is the use of commutator?
send me all basic electrical question and answers
1 Ton is equal to how many watts?
HOW TO WORK A VFD?SAY SIMPLE METHOD
Why auxiliary transformers are not connected in parallel in primary stations?
What are the three major categories of error?
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?