Answer Posted / william lobo
For PX class CTs , the burden is not normally mentioned .
There the CT is defiened based on the CT kneepoint
voltage , magnetising current etc . The burden is mentioned
in class P CTs
In PX class CTs the kneepoint voltage is normally based on
the max fault current and a diamensioning factor based on
system X/R ratio
| Is This Answer Correct ? | 3 Yes | 3 No |
Post New Answer View All Answers
ht side line to earth voltage
What is current divider rule (cdr)?
iam using DM 3251 voltmeter(1 percent accuracy)for 11KV system PT ratio is 11KV/110V.can anybody explain what is the max and min voltage deviation.
when we design electrical schemes of 11/.415kv distribution..wen and were should we show the relays??what is the function of it?for example..we place EFR Relay CT between transformer neutral link and transformer earth.Like this what are the other type of relays we should use?why?where?Explain please..Thank you
what is differnce btwen lll and lllg faults
what is the difference between 4pole & 6pole DC Motors & give advantage ?
what & how to check the lightning arrester
why induction motors are rated at 0.8 power factor.
Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?
What are the two segments of nyquist contour.
What is the formula to calculate the rating of a three phase miniature circuit breaker
what r the checklist while installing 500 kva transformer
What are the main significances of root locus?
what is the meaning of number in (11, 31, 61,14, etc. CDG11, CDG31, CDG61, DDT32
What is the function of NER and NET?