the distance from my office to d.g is aprox 400mtrs and
voltage drops ibn my office near about 40 volt what should
i do p[ls suggest.
Answers were Sorted based on User's Feedback
Answer / ps win
The drop in voltage from the origin of the circuit to any point in the circuit should not be more than 4% of the nominal voltage. I would like to suggest you that you should re-size the cable.
Is This Answer Correct ? | 4 Yes | 0 No |
Friend
You can either shift ur DG near to ur office, or u change
the size of the cable connecting from DG terminal to switch
board, preferably with a copper cable. Present cable size
is very low compared to the distance and the load taken by
the cable, and hence u have a voltage drop of 40V.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ssreenu
please tell me why we can't use capacitors in DG power?
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ps win
(+ or - 4% of nominal voltage can be acceptable.)
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / sree
Add capacitors in load side, which improves your PF as well
as voltage.
Is This Answer Correct ? | 0 Yes | 2 No |
Describe kW and kva and difference between
why tan delta test is carried out in the power transformer? which parameter are measure?
Can any horizontally mounted motor be used as vertical?
my diploma certificate in my higher education college
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
Reason of secondary of ct always short
In an ideal transformer no load primary current I0 A lags behind V1 by 90 degree B is in the phase with V1 C leads V1 by 90 degree D lags V1 by 45 degree
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
which motors is used in mixies
circuit breaker work alone during fault condition or need any relays ?
What does the temperature (30 deg or 35 deg celcius) mark on conservator of transformer indicates?
I NEED RRB SYLABUS FOR JE ELECTRICAL ,PLEASE SEND TO MY E- MAIL ID joo28_eee@yahoo.co.in