if a damaged 500kva transformer with %impedance 2.6 is
replaced by two transformers of 250Kva with different %
impedance will they be able to catter the load. what will
be the ratio of load on the two transformers if the %
impedance is in the ratio 1:2
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The above is correct.But transformers with same capacity and
voltage having % impedances in the ratio 1:2, is not
believable.The load sharing will be in 2:1 ratio if they are
connected in parallel.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / aamod tripathi
This should not be done ideally (Parallel operation not
permitted) . However the load can be distributed exclusively
and independently on each transformer (Each Transformer
connected to indivisual (incomer) feeder and independent
loads(outgoing))
| Is This Answer Correct ? | 4 Yes | 5 No |
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
how do we fix the rating of mcb required for a specific capacity of the electric motor
in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?
Differentiate between Zero and Negative sequence current
what is grounding & what is the value of groumding rod 2.5m?
how a generating station can monitor its multi users power factor. What type of incentive /penalty is associated with power factor management.
like the transformer another electrical static device which operate on same priencipal?
13 Answers Power Grid, Vishal Transformers,
What is transposition in a transmision line?
URGENT PLEASE//////////A WORK SHOP IS HAVING A 100 KVA TRANSFORMER 11KV/415 VOLTS, AND THE CONNECTED LOAD OF THE WORK SHOP IS 80 KW WITH INDUCTIVE LOADS, LIGHTING LOADS,ETC., HOW MANY EARTH ELECTRODES ARE NEEDED AND WHAT IS THE EARTH RESISTANCE OF EACH EARTH ELECTRODE AND COMBINED EARTH RESISTANCE in normal soil. AT 11 KV SIDE AND AT LT SIDE. HOW TO CALCULATE.
what is the difference between fault current ant short circuit current?
As per principle we say in three phase supply ,the voltage is producing by phase angle between two phase so two phase is needed means then why we using three phase ?
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)