if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with..

Answer / k.prakashchandra

The above is correct.But transformers with same capacity and
voltage having % impedances in the ratio 1:2, is not
believable.The load sharing will be in 2:1 ratio if they are
connected in parallel.

Is This Answer Correct ?    3 Yes 2 No

if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with..

Answer / aamod tripathi

This should not be done ideally (Parallel operation not
permitted) . However the load can be distributed exclusively
and independently on each transformer (Each Transformer
connected to indivisual (incomer) feeder and independent
loads(outgoing))

Is This Answer Correct ?    4 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

what is the full form of ka (100A mccb KA)

1 Answers  


what is class of SPD and dittels of all class ?

0 Answers  


explain the types of drives

0 Answers  


What will happen if the voltage in my house drops from 220V to any lower voltage?

0 Answers  


Dear all, is ther any body who can tell me about the setting of ACB(air circuit breaker ). what kind of it,s setting is and how to do it,s setting. also please tell me the setting of VCB(vaccume circuit breaker) . please tell me their setting,s. i will b very thank ful to all of u. Thank,s and Regard,s. Muhammed Ikram.

2 Answers  






what is difference between power transformer and distribution transformers

1 Answers  


how to differentiate a mpcb,mcb with a contactor? Explain their working operation

0 Answers   L&T,


Brief working principle of stabilizer,application & safety precautions

0 Answers  


why tan delta test is carried out in the power transformer? which parameter are measure?

1 Answers  


What happen when increese more than 50HZ fequincy.

5 Answers  


10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.

1 Answers   Engro,


How do ACB are maintenance, what are the problem occurred in ACB

1 Answers   KIML,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)