Answer / mathan
loop checking means ,after installation of instruments we
must check full loop(instrument-junction box-control room)
to ensure that whether the instruments are working properly
or not, and whether is it passing the signal or not,whether
is it receiving the signal or not. before we start the
plant we need to check loop..
during the loop check we give some known input
and check the corresponding output at other side(control
room)..if the output is corresponding to input, the loop is
ok..if not means, something fault inbetween the loop.
for example.if you want to check ON/OFF control
valve,during the loop check,when you give 24v dc from
control room ,the valve must open fully, and when you give
0v dc the valve must close.
| Is This Answer Correct ? | 274 Yes | 10 No |
Loop Checking means, First we want to check the continuity
of cable. Then whether 24 V DC or 4 - 20 mA DC is coming
from DCS or JB want to check. That is called loop Checking.
| Is This Answer Correct ? | 132 Yes | 18 No |
Answer / rovel delalamon
loopcheking, field to the control room.from instruments to ijb.formijb to mrashalling cabiet.,,check polarities,check the voltage suplly w/24v dc. chech also the possible leaks of the tube.and warm-up 5mins.prior to calibration.use HART COMMUNICATOR.highway addressable remote transducer.the one who configuer the input and output of the trnsmitter
| Is This Answer Correct ? | 42 Yes | 17 No |
Answer / shreeyash nandurkar
Loop Checking
Some think of loop checking as
a process to confirm that the
components of the loop are wired correctly and is typically
something
done prior to start-up. However,
due to factors described in the
introduction above, the loop check’s
scope has expanded to also include
tests to confirm that it is “operating as designed” and then
to ongoing
programs for benchmarking and monitoring performance. The block
diagram in Figure 1-5 illustrates the
components of this expanded loop
checking process.
This process starts when the instruments are received at the
plant site.
It continues through installation and
start-up and into the ongoing plant
operation. In addition, the control system should perform
the intended
function properly. This includes
verifying the transmitter’s process
variable (PV) for display to the operator, for use in the
control strategy,
and for historical trending. This verification testing prior
to start-up is
known as the factory acceptance test
(FAT) which, as an option, can be
duplicated at site with the actual hardware and software
installed, termed
site acceptance test (SAT). Further discussed in Chapter 2,
the FAT can be
performed prior to shipment of the
hardware or in parallel with the
hardware installation
at site if the overall start-up schedule is compressed.
Once the technician checks the control strategy to verify
that the
expected output to the final control element is produced,
the loop can then
be commissioned and start-up can proceed.
Finally, the loop check can include defining the loop
performance
benchmark and providing a method for monitoring the
performance over
time.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / md mahtab khan
loop checking as a process to confirm that the
components of the loop are wired correctly and is typically something done prior to start-up.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / rodel baluyot
LOOP CHECKING IS CHECKING 4 TO 20 MA OUTPUT FIELD AND CONTROL ROOOM
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / azarudeen
Loop checking is nothing but Checking continuity.
| Is This Answer Correct ? | 20 Yes | 72 No |
Answer / surya
I think loop checking is another way of calling "feedback"
...
m not sure abt it..
| Is This Answer Correct ? | 19 Yes | 81 No |
how checking is done in fiber optic cable? explain the working of RTU?
Pressure transmitter working Principles?
IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?
what is the difference between Digital output DO signals /Commands for start/stop and Solenoid valves ??
My flow transmitter range is 0-1000mmwc.DCS range is 0- 100m3/hr.What is correspond out put in terms of milliamps if my flow is 65m3/hr
what is reason behind boiler drum level transmitter range put -450 to 0 mmh2o.
HELLO FRIENDS PLZ EXPLAINE ME WHAT IS ORIFICE?AND HOW WE ARE USING IT IN INSTRUMENTATION
what are the problem's will accure in dcs or plc hadware and what are the solution for it?
Ega interview going on for power plant. Which type of question will asked. For questions
Difference between guide wave radar & non guide wave radar ?
how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)