what is reason behind boiler drum level transmitter range put
-450 to 0 mmh2o.
Answer / carl_ellis
Water vapor in a vessel (like a boiler drum) will condense
in piping/tubing attached to the upper tap. The condensed
water collects in the piping/impulse tubing connected to the
transmitters low side port.
The water exerts a pressure on the transmitter's low side
port. If the liquid columns stays at the same height, then
it can assumed to be a constant which can be used as part of
the level calculation.
So boilers use a 'wet leg' where the low side leg is
deliberately filled with fluid and is expected to remain at
a constant level.
A differential pressure level transmitter works by
subtracting the low side from the high side.
DP = high side - low side
In this case, the low side liquid column of water exerts a
pressure of 450 mm wc. wc = water column
When the drum is empty,
the high side measures 0 pressure, 0 mm wc.
the wet leg measures 450 mm wc.
DP = high side minus low side
DP = 0 mm - 450 mm = -450 mm wc
When the drum is full, the high side pressure will be (steam
pressure + 450 mm wc) where the 450 mm wc is the water
column in the drum.
The low side pressure will be (steam pressure + 450 mm wc)
where the 450 mm wc is the water column in the low side
impulse tubing/piping.
DP = high side minus low side
DP = (steam pressure + 450 mm wc) - (steam pressure + 450 mm
wc) = 0 mm wc
So empty = -450 mm wc, full = 0 mm wc.
The transmitter's range is -450 to 0 mm wc.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
how to calibrate level transmitter
Explain how thw analog to digital converter works with the circuit diagram
What is the difference between compensation and extension cable.
give me all the details about the interview and which type of question being asked
What is DCS?
why we are using drum level control valve air to close?
A flange is used for instrument connection for a system with a design temperature of 316C (600F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer
How to adjust the zero & span of a control valve from the posiitioner(MIL)?
any body who gone thru recent iocl interview.INSTRUMENTATION questions. I need.
1. For Steam drum level signal, why do we compensate with drum pressure signal? 2.For main steam Flow signal is comensated with main steam temperature signal and main steam pressure signal why?
1)How many tpes of vibration probe and how many tpyes of vibration. 2)how we can calibrate a vibration probe with tk3 3)what is RMS value in vibration measuring application and how we calculate it.
how many type conductivity sensor ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)